Size of PCT Project folder is increasing

Size of PCT Project folder is increasing

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Issue

PCT project folder size increases when an object is deleted.

Product Line

EcoStruxure Building Operation

Environment

Project Configuration Tool, PCT

Cause

Any change made in PCT increases the size of PCT project folder. This is by design and it is a normal behavior of PCT.

The reason for this is that a project is a virtual machine using a dynamically allocated image that grows when memory is needed, but the image will not shrink when something is deleted. 

Resolution

The only way to reduce the folder size of a project is to backup all servers in the project, create a new project, restore the server backups to the new project and then delete the old project.