  • Powerlogic PM5320 http access and DDF for DCE 7.5
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49522members
Join Now
242868posts
Join Now

Powerlogic PM5320 http access and DDF for DCE 7.5

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:44 PM
0 Likes
12
120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:44 PM

Powerlogic PM5320 http access and DDF for DCE 7.5

This question was originally posted on DCIM Support by shemilusman on 2018-09-18


Hi Support,

We have Powerlogic PM5320 connected to DCE Server 7.5 through the private LAN connection. I have assigned IP address to the meter but I am only able to ping the device and not able to access the device using any browser (http access not available).

In the comm port it is showing BACnet which I believe should be Modbus.

I am trying to Add the device in DCE 7.5 using snmp v1 and not working. No browser is also supported. Please if someone can assist.

I also need the DDF file for Powerlogic 5320.

Thanks & Regards

Shemil

 

 

(CID:134033220)

Labels
  • Data Center Expert
  • DDF
Share
  • All forum topics
  • Previous Topic
  • Next Topic
12 Replies 12
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:44 PM
0 Likes
7
120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:44 PM

Re: Powerlogic PM5320 http access and DDF for DCE 7.5

This answer was originally posted on DCIM Support by Steven Marchetti on 2018-09-18


Hi,

 

If you choose the device support menu above:

http://sxwhelpcenter.ecostruxureit.com/devices

You can search for available DDF files. You can also request a new DDF if there are none available for your device. There is also a video on that page that explains the process.


Thanks,

Steve

(CID:134033246)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:44 PM
0 Likes
0
120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:44 PM

Re: Powerlogic PM5320 http access and DDF for DCE 7.5

This comment was originally posted on DCIM Support by shemilusman on 2018-09-18


Hi Steve,

Can you please reply why the http access is not working for this meter, even after assigning an IP Address? Also I am not able to add the device in DCE 7.5

For the DDF, the device support says its supported but the DDF is not available to download.

Thanks

Shemil

 

 

(CID:134033261)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:44 PM
0 Likes
0
120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:44 PM

Re: Powerlogic PM5320 http access and DDF for DCE 7.5

This comment was originally posted on DCIM Support by Steven Marchetti on 2018-09-18


Sorry, thought you needed the DDF.

The first issue I can see that you might be having is that the device is that you're showing a bacnet configuration.  It must be configured for either modbus or SNMP for DCE to be able to discover it. What is the modbus setting on the unit?

I don't have one of these meters specifically but there should be a modbus configuration in that same control panel where you're showing the bacnet info. If you can't find it, You can try checking out the manual here:

https://www.schneider-electric.com/en/download/document/EAV15107-EN/

I do not believe there is a web page for the device. If you need more device specific info, you may want to contact the PowerLogic specific support as this page is more geared toward StruxureWare DCO and DCE. The link above also has contact info.

 

Thanks,

Steve

(CID:134033280)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:44 PM
0 Likes
0
120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:44 PM

Re: Powerlogic PM5320 http access and DDF for DCE 7.5

This comment was originally posted on DCIM Support by shemilusman on 2018-09-18


Hi Steve,

I don't see any Mobdus page but only BACnet configuration is available. Only BACnet Status can be changed "enabled or disabled"

and no option to choose Modbus protocol.

Thanks

Shemil

(CID:134033291)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:45 PM
0 Likes
0
120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:45 PM

Re: Powerlogic PM5320 http access and DDF for DCE 7.5

This comment was originally posted on DCIM Support by Steven Marchetti on 2018-09-18


 

Hi Shemil,


Yes, I just looked through the manual and it appears that there isn't a Modbus config:

If you're set on using DCE with this, all I can suggest is to use a meter that does support this feature or potentially find a bacnet to modbus gateway to translate so DCE can monitor it.


Steve

(CID:134033306)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:45 PM
0 Likes
0
120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:45 PM

Re: Powerlogic PM5320 http access and DDF for DCE 7.5

This comment was originally posted on DCIM Support by shemilusman on 2018-09-18


Hi Steve,

But I am using the Ethernet port and its mentioned "with Modbus TCP" in the manual screen you send. So do you think if I upload the DDF I will be able to discover the meter as a Modbus TCP device?

Thanks

Shemil

 

(CID:134033319)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:45 PM
0 Likes
0
120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:45 PM

Re: Powerlogic PM5320 http access and DDF for DCE 7.5

This comment was originally posted on DCIM Support by Steven Marchetti on 2018-09-18


Hi Shemil,

The column that I highlited shows a blank or "-" where the modbus option is. I did highlight the correct model, yes? Add to that the fact that you are not able to configure modbus port, slave ID or enable/disable as per your own comments, it would appear that this unit is not capable of Modbus. Again, Powerlogic support may be able to verify this for you but adding a DDF will not help if you don't know what slave ID to use or if it doesn't speak modbus at all. 


Steve

(CID:134033339)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:45 PM
0 Likes
0
120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:45 PM

Re: Powerlogic PM5320 http access and DDF for DCE 7.5

This comment was originally posted on DCIM Support by shemilusman on 2018-09-24


Hi Steve,

We uploaded the DDF for the PM5300 meter and its working now.

Thanks

Shemil

(CID:134035131)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:45 PM
0 Likes
0
120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:45 PM

Re: Powerlogic PM5320 http access and DDF for DCE 7.5

This comment was originally posted on DCIM Support by spezialist on 2018-10-07


Dear shemilusman,

Tell us, please, did you solve your problem or not?

With respect.

(CID:134680006)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:45 PM
0 Likes
0
120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:45 PM

Re: Powerlogic PM5320 http access and DDF for DCE 7.5

This comment was originally posted on DCIM Support by shemilusman on 2018-10-08


Hi,

We uploaded the DDF for the PM5300 meter and its working and problem solved.

Thanks

Shemil

(CID:134680195)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:45 PM
0 Likes
0
120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:45 PM

Re: Powerlogic PM5320 http access and DDF for DCE 7.5

This comment was originally posted on DCIM Support by spezialist on 2018-10-08


Ok, very thanks for the good feedback 😀.

(CID:134680205)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 11:45 PM
0 Likes
0
120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 11:45 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric