The DCE is showing that the link status for the NetBotz and Sensor Pods are offline even though they are up. I can log onto each NetBotz via the Advanced View.
(CID:132668585)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:46 PM . Last Modified: 3 weeks ago
Dear Krista Flynn,
I assume that you mean NetBotz-4.x appliance?
The reasons for your problem can be many, so first of all, my first question: have you recently changed your login/password for accessing to the NetBotz appliance? Verify the correctness of NetBotz Appliance Credentials... in DCE software.
Did you change the web-access protocol in the NetBotz appliance settings (HTTP or HTTPS)?
In general, did you change the network settings of your NetBotz appliance?
After what events or changes do you have the above problem with your NetBotz appliance?
With respect.
(CID:132668787)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:46 PM . Last Modified: 3 weeks ago
I was able to remove the netbotz devices and re-add them after talking with a technician. Things are working as they are supposed to!
(CID:133370434)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:46 PM . Last Modified: 3 weeks ago
Ok, however, it could not be deleted, but simply perform a re-discovery. This should also work.
Thanks for the feedback 😀.
(CID:133370436)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:46 PM . Last Modified: 2023-10-22 02:57 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.