Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • ITA 9.1.0 - Energy Cost Report
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49246members
Join Now
242459posts
Join Now

ITA 9.1.0 - Energy Cost Report

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
Gianluca
Lieutenant JG Gianluca Lieutenant JG
Lieutenant JG
‎2020-08-30 11:32 PM
0 Likes
12
862
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-30 11:32 PM

ITA 9.1.0 - Energy Cost Report

Hi All

 

last week i have upgrade a Dco to ITA 9.1.0.

backup ad restore was ok.

 

how long customer have to wait to generate Energy Cost Report?

 

thanks a lot

Labels
  • Data Center Operation
  • DCIM Support
  • IT Advisor
Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
12 Replies 12
gsterling
Lt. Commander gsterling Lt. Commander
Lt. Commander
‎2020-08-31 04:21 AM
0 Likes
11
847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-31 04:21 AM

Re: ITA 9.1.0 - Energy Cost Report

Hello Gianluca.

 

Are you saying your customer does not see the EnergyCost report after the upgrade to ITA?

 

Has the customer tried opening the reports view, and restoring the default designs? This is sometimes necessary.

 

Here is a screenshot of the view I'm referring to from the reports view in the desktop client. Its likely this will cause the energy cost report to appear.

 

RestoreDesigns.JPG

 

Regards

 

Greg Sterling

 

Tags (1)
  • Tags:
  • english
Share
Reply
Gianluca
Lieutenant JG Gianluca Lieutenant JG
Lieutenant JG
‎2020-08-31 04:24 AM
0 Likes
10
844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-31 04:24 AM

Re: ITA 9.1.0 - Energy Cost Report

Hi Greg

 

not that

 

customer can generate report but without data

 

how long customer have to wait to generate Energy Cost Report?

 

thanks

 

Tags (1)
  • Tags:
  • english
Share
Reply
gsterling
Lt. Commander gsterling Lt. Commander
Lt. Commander
‎2020-08-31 04:29 AM
0 Likes
9
842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-31 04:29 AM

Re: ITA 9.1.0 - Energy Cost Report

What are they seeing in the report output?

 

Do they see their racks but the measurements are showing as 0's?

 

Regards

 

Greg Sterling

Tags (1)
  • Tags:
  • english
Share
Reply
Gianluca
Lieutenant JG Gianluca Lieutenant JG
Lieutenant JG
‎2020-08-31 04:44 AM
0 Likes
8
838
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-31 04:44 AM

Re: ITA 9.1.0 - Energy Cost Report

Hi Greg

 

i cannot see any measurements on rack.

 

with Dco v8.2.2 and same license, customer was able to generate it

 

Tags (1)
  • Tags:
  • english
Share
Reply
gsterling
Lt. Commander gsterling Lt. Commander
Lt. Commander
‎2020-08-31 04:56 AM
0 Likes
7
836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-31 04:56 AM

Re: ITA 9.1.0 - Energy Cost Report

Can you send a screenshot or sample report output?

 

There is a bug which was recently found in the newer ITA releases which effects the EnergyCost report and its output. In the case I know about it was causing 0's to be reported where there should have been measurement data for at least some rackpdus. The bug was definitely centered on how measurement data is displayed in the report. This bug is expected to be fixed in 9.1.1 which is due in the near future.

 

What types of devices are in these racks and are their measurements collected from DCE? Can you share sample report output too?

 

Regards

 

Greg Sterling

Tags (1)
  • Tags:
  • english
Share
Reply
Gianluca
Lieutenant JG Gianluca Lieutenant JG
Lieutenant JG
‎2020-08-31 05:03 AM
0 Likes
6
834
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-31 05:03 AM

Re: ITA 9.1.0 - Energy Cost Report

Hi Greg

 

could i talk to you by Teams?

 

i will show you report

Tags (1)
  • Tags:
  • english
Share
Reply
gsterling
Lt. Commander gsterling Lt. Commander
Lt. Commander
‎2020-08-31 05:14 AM
0 Likes
5
831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-31 05:14 AM

Re: ITA 9.1.0 - Energy Cost Report

Yes

Tags (1)
  • Tags:
  • english
Share
Reply
Gianluca
Lieutenant JG Gianluca Lieutenant JG
Lieutenant JG
‎2020-09-16 08:00 AM
0 Likes
4
657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-16 08:00 AM

Re: ITA 9.1.0 - Energy Cost Report

Hi

about the issue, customer said that he can see all the info for september but still no data for August

Tags (1)
  • Tags:
  • english
Share
Reply
Jef
Commander Jef Commander
Commander
‎2020-09-17 05:52 AM
0 Likes
3
643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-17 05:52 AM

Re: ITA 9.1.0 - Energy Cost Report

Hi Gianluca,

 

I will send you an invite to my =S= box shortly, just in case if you would be able to provide the following data:
1- latest backup file from 9.1 setup
2- complete server logs from 9.1 setup
3- screen capture of the issue report (full screen)
4- 8.3.2 backup file, which is used for the upgrade to 9.1
5- server logs from 8.3.2 setup (if that is possible)

then I will see what I can find.

Kind regards,

Jef

Tags (1)
  • Tags:
  • english
Share
Reply
Gianluca
Lieutenant JG Gianluca Lieutenant JG
Lieutenant JG
‎2020-09-18 05:05 AM
0 Likes
2
615
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-18 05:05 AM

Re: ITA 9.1.0 - Energy Cost Report

Hi Jef

 

im uploading files

Tags (1)
  • Tags:
  • english
Share
Reply
Jef
Commander Jef Commander
Commander
‎2020-09-21 03:43 AM
0 Likes
0
604
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-21 03:43 AM

Re: ITA 9.1.0 - Energy Cost Report

Thanks Gianluca,

I will look into the data and will get back to you asap,

Kind regards,

Jef

Tags (1)
  • Tags:
  • english
Share
Reply
Jef
Commander Jef Commander
Commander
‎2020-09-24 12:19 AM
1 Like
0
594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-24 12:19 AM

Re: ITA 9.1.0 - Energy Cost Report

Hi Gianluca,

Thanks again for providing data, I could follow and confirm your observations. Here is a short explanation why your energy cost reports (in 9.1) not showing the data as you've expected. In latest release versions including DCO 8.3.x and ITA 9.0.x/9.1 we started to distinguish measured values for whole devices from measured values for device banks. The changes was not applied to Energy Cost report. This resulted in only measurements for banks being visible in report. The problem is that your solution has only measurements for devices, so report has no knowledge of their existence and assumes 0 kWh.
This is resolved in ITA 9.1.1.
I will also contact you by direct email soon.

Kind regards

Jef

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
MateFekete
Crewman MateFekete
1
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric