Hi,
Can we get DCE alarm shown in DCO faster? From setting, looks like we are limited to 5 minutes polling interval. (Full Alarm synchronization time)
Thank you.
(CID:103585776)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:42 PM . Last Modified: 3 weeks ago
Hello Ling,
Generally speaking the time frame from my testing is approximately 30 secs from when DCE gets an alarm to DCO seeing the alarm. A few things that I would recommend checking
As well as, DCO relies on the network for HTTP/HTTPS requests. If there is alot of traffic on the network we may see slow response to new or clearing alarms.
Thanks
Victor
(CID:103585830)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:42 PM . Last Modified: 3 weeks ago
"Update Device information" does not influence how quick alarms are send. Reducing it is not a good idea.
(CID:103585844)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:42 PM . Last Modified: 3 weeks ago
The DCE will push new alarms to DCO more or less immediately after it receives an alarm. The DCO will on a regular interval load all alarms from DCE to guard against communication lost etc. in the push. The latter is the Full Alarm synchronization time.
So unless there's network communication issues, "Full Alarm synchronization time" does not influence how quick new alarms are received in DCO.
(CID:103585843)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:42 PM . Last Modified: 2023-10-31 10:59 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.