This question was originally posted on DCIM Support by Gleb Tyunikov on 2018-08-30
Hello guys,
I ran into a bit of a problem..
First of all in my Data Center i have few hot aisle containment pods, and we have inrow's for cooling.
After the placement of the racks and the inrows in a closed aisle I can see in the cooling tab that all racks are green - they all getting enough cooling.
I have yet to install my temperature sensor so i want to see the calculated map in the 3D veiw model.
When i try to see it, it throws me this message "Floor tile airflows did not add up to downflow CRAC airflows
I've read in other threads that this happens when you use non apc inrow, and so I changed it and placed an apc ones instead and still, i get this Error message..
Could you please help me to find the solution to this?
Thank you,
Gleb Tyunikov
(CID:134024383)
Solved! Go to Solution.
This answer was originally posted on DCIM Support by Jef Faridi on 2018-08-30
Hi Gleb,
As illustrated in the following image, I have used one "InRow RC 300mm Standard" unit without any problem:
I think to understand your issue, I would need more details about the setup - can you provide a copy of your backup file (shared safely with me)?
Kind regards
(CID:134024443)
This comment was originally posted on DCIM Support by Jef Faridi on 2018-08-30
Hi Gleb,
Can you please share screen captures illustrating which cooling units/part numbers (from Genome Library) you are using, thanks.
Kind regards
(CID:134024422)
This comment was originally posted on DCIM Support by Gleb Tyunikov on 2018-08-30
Hi jeff,
Unfortunately i cant share a screenshot
But I'm using the APC 300mm standard units
Thank you
(CID:134024428)
This answer was originally posted on DCIM Support by Jef Faridi on 2018-08-30
Hi Gleb,
As illustrated in the following image, I have used one "InRow RC 300mm Standard" unit without any problem:
I think to understand your issue, I would need more details about the setup - can you provide a copy of your backup file (shared safely with me)?
Kind regards
(CID:134024443)
This comment was originally posted on DCIM Support by Gleb Tyunikov on 2018-08-30
Well as i said earlier its not possible to share any screenshots or backup files..
But I will be more than happy to provide you with specific technical information...
What is strange to me in my situation is that in the cooling tab i can see that the racks are getting cooled and are using right temperatures and only the 3D representation wouldn't work..
When the InRow is placed, is there any specific information that has to stay written on it? like in your picture the "manufacturer" "model" any else?
(CID:134024456)
This comment was originally posted on DCIM Support by Jef Faridi on 2018-08-30
Hi Gleb,
I was able to reproduce:
As illustrated, if I customize a copy of my InRow cooling unit (by replacing APC with another manufacture) in my Genomes. And then drag this to the floor and run 3D temp calculations, then I see a similar notification as you've mentioned:
I will capture a bug report for this.
Workaround:
If I use the InRow cooling unit (without modification) and drag it to the floor:
And then change the manufacture name for this unit on the floor:
Now I can run the 3D temperate simulation without any problem:
Kind regards
(CID:134024488)
This comment was originally posted on DCIM Support by Gleb Tyunikov on 2018-08-30
Amazing,
Thank you very much Jeff
have a great day!
(CID:134024496)
This comment was originally posted on DCIM Support by Jef Faridi on 2018-08-30
You are most welcome, Gleb
have a great day, too
thanks.
Kind regards
(CID:134024499)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Discuss challenges in energy and automation with 30,000+ experts and peers.
Find answers in 10,000+ support articles to help solve your product and business challenges.
Find peer based solutions to your questions. Provide answers for fellow community members!