I update FW UPS symmetra MW after that DCE alarm DDF failed .
Symmetra MW FW 25.20
Display FW3.6.3.102_3.6.3.102a
DCE Ver 7.5.0
I want to monitor UPS on DCE by SNMP
Please ,advise.
(CID:146670587)
Solved! Go to Solution.
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-07-07
Hi,
the device status error can be fairly easily resolved by following the linked kbase,
https://www.apc.com/us/en/faqs/FA177004/
Please note that for the Symmetra MW however you will likely get much more information by monitoring it using Modbus.
Thanks,
Steve.
(CID:146670600)
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-07-07
Hi,
the device status error can be fairly easily resolved by following the linked kbase,
https://www.apc.com/us/en/faqs/FA177004/
Please note that for the Symmetra MW however you will likely get much more information by monitoring it using Modbus.
Thanks,
Steve.
(CID:146670600)