Same input able to be used twice:
I'm having trouble replicating this to get the exact pattern, but
i'm sometimes able to make a temperature input and a digital
input the same Ub input number.
Ub input missing from list when multiple points deleted.
When deleting inputs, and then bringing in new ones, there
tends to be a Ub missing from the list when that point should
be freed up. If you choose any other Ub, then the missing
Ub input will be choosable again the next time you want to select
an input channel.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-09-22 12:26 PM
The issue with the disappearing/reappearing terminals is reproducible and has been logged as a defect with Tridium.
The issue where you have the ability to assign the same terminal to two objects - not so easy to reproduce.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-09-11 09:45 AM
I have seen inconsistent results with this as well. We have not been able to replicate this, so it has not been submitted as a defect yet. Once the results are able to be duplicated we can submit it as a defect. Any help on this issue would be greatly appreciated.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-09-22 12:26 PM
The issue with the disappearing/reappearing terminals is reproducible and has been logged as a defect with Tridium.
The issue where you have the ability to assign the same terminal to two objects - not so easy to reproduce.
Link copied. Please paste this link to share this article on your social media post.