I couldn't get that although bank 1 and bank 2 currents of a rack display "0 A" phase1 current displays" 0.5 A".What do those display.Thanks in advance.
(CID:126180743)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:22 AM . Last Modified: 3 weeks ago
Hi Ibrahim, Are you referring to rPDU Bank 1 and Bank 2 current dislay? If so, it depends upon the accuracy of rPDU Bank current display. If it is total current 32 Amps Single Phase PDU, then it does have two banks of outlets groups which is normally limited by 16 Amps per outlet groups.
Phase current=Total rPDU current
Bank Current=Two Banks Current of PDU
The bank current may show if the current of the phase is more than 1 Amps as it may depend up the PDU make, model number and accuracy level.
I hope it helps.
Regards,
Bala
(CID:126180770)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:22 AM . Last Modified: 3 weeks ago
Hi Ibrahim, Are you referring to rPDU Bank 1 and Bank 2 current dislay? If so, it depends upon the accuracy of rPDU Bank current display. If it is total current 32 Amps Single Phase PDU, then it does have two banks of outlets groups which is normally limited by 16 Amps per outlet groups.
Phase current=Total rPDU current
Bank Current=Two Banks Current of PDU
The bank current may show if the current of the phase is more than 1 Amps as it may depend up the PDU make, model number and accuracy level.
I hope it helps.
Regards,
Bala
(CID:126180770)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:22 AM . Last Modified: 3 weeks ago
Thanks for the fast response and clear answer.
(CID:126180806)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:22 AM . Last Modified: 3 weeks ago
You are welcome Ibrahim!
(CID:126180810)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:22 AM . Last Modified: 2023-10-22 04:18 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.