We got a trouble with upgrade DCE 7.2.2 to 7.2.4.
Customer have installed DCE 722 VM. We trying to upgrade server.
When we import 7.2.4 upgrade file in serverupgrade dialog menu in DCE client - it's ok.
Then system goes to restart and open browser with next page.
Without any information about upgrade. ☹️
What can gone wrong?
(CID:110004668)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 07:49 AM . Last Modified: 3 weeks ago
Hi Anton,
This could be caused by insufficient space on the VM disk. See KBase FA290375 for more information about this.
If adding another disk to the VM does not help, there may be another underlying issue. In that case, you should contact your local Support, and provide them with the latest capturelogs from the server.
Regards
John T
(CID:110004671)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 07:49 AM . Last Modified: 3 weeks ago
Hi Anton,
This could be caused by insufficient space on the VM disk. See KBase FA290375 for more information about this.
If adding another disk to the VM does not help, there may be another underlying issue. In that case, you should contact your local Support, and provide them with the latest capturelogs from the server.
Regards
John T
(CID:110004671)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 07:49 AM . Last Modified: 2023-10-22 04:12 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.