Dear Team,
We have connected following brands of UPS with data center expert server:
Data Center Expert is not reporting correct sensors status of all brands. It is reporting correct sensors values only of APC.
How to resolve this issue?
Best regards,
Nadeem Ansari
(CID:110013795)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:45 AM . Last Modified: 3 weeks ago
Hello nansari
Are the sensors reporting incorrect values or Unplugged or another status?
DCE 7.2.0 is several versions behind the current version 7.4.2, so you should contact your local Technical Support to validate your software support contract in order to get the links to upgrade.
If upgrading the DCE does not resolve this, you may need to contact the Device Support team for the latest DDFs for those 3rd party devices. You can check for and request DDFs using the link below.
https://dcimsupport.apc.com/devices
Regards
(CID:110013812)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:45 AM . Last Modified: 3 weeks ago
Dear Nadeem,
Struxureware Data Center Expert software comes with pre-loaded Device Definition File(DDF) for APC products to show the parameters correctly under view device sensors.
Regarding third party products sensors values, we need to add the appropriate DDF file for DCE to recognize and show the correct sensors values depending upon the device capability which are supported via either SNMP or Modbus Over TCP.
I request you to verify if the correct DDF file is added to DCE software for third party products. You can also request the DDF file on EcoStruxure IT Help Center.
Please refer the DDF request procedure here.
Once you add the right DDF file, your problem will be resolved.
I hope this helps. Please share screen shots if my answer does not answer your query.
Regards,
Bala
(CID:110013814)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:46 AM . Last Modified: 2023-10-22 03:58 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.