Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
Security Vulnerabilities for older APC equipment
EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-11-0411:59 AM
Security Vulnerabilities for older APC equipment
Hi,
A client running EcoStruxure IT is looking at resolving some security issues linked to older hardware that is still in use. The hardware includes ACRD502s, AP7821s & a Symmetra UPS. These all do not have TLS1.2
Unfortunately we have not been able to find newer firmware for these units and would like to find out is there is anything that can be done as the units are still functioning properly and the client is not looking at refreshing them anything soon.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-11-0912:31 AM
Hi Kevin,
I can't speak for the cooler but the AP7821 is based on the NMC1 and it is possible that the Symmetra also has an NMC1.
The NMC1 is quiet old and due to hardware limitations it only support TLS1.0.
In terms of corrective action an NMC2 can also be installed in a Symmetra and is capable of TLS1.2 but is going end of sale soon (it will still be supported for several year). At present the newer NMC3 only supports single phase Symmetra products but I believe it will support three phase units shortly.
Unfortunately the network card in the PDU is not upgradable.