Hi there,
Is it possible to mix wireless and wired sensors? How many of each one together? To use the maximum of sensors, is it necessary a power supply (AP9505i)?
To use three or more handles, is it possible to use a NBRK0250 just as a "sensor pod" for handles?
Thanks, masters!
(CID:113642846)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:37 PM . Last Modified: 3 weeks ago
Hi Anders,
If you need more than 2 handles, you will either need to get a second 250 or you'll need to go with something like the 570 with rack access pods NBPD0171.
You can mix wired and wireless.
The quick config guide is here:
http://www.apc.com/salestools/JLER-A4CL7S/JLER-A4CL7S_R0_EN.pdf
It notes up to 47 wireless sensors
Up to 8 A-link sensors AP9520T/TH
Maximum number of NBPD0150 sensor pods is 6...each capable of connecting 6 wired sensors in addition to the ports available on the unit itself.
The 95051 is recommended in larger configurations. I believe it is stated that one for every 4 pods but depending on where you have it installed (interference) and how far away the pods are, you may need to use more.
Steve
(CID:113642903)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:37 PM . Last Modified: 3 weeks ago
Hi Anders,
If you need more than 2 handles, you will either need to get a second 250 or you'll need to go with something like the 570 with rack access pods NBPD0171.
You can mix wired and wireless.
The quick config guide is here:
http://www.apc.com/salestools/JLER-A4CL7S/JLER-A4CL7S_R0_EN.pdf
It notes up to 47 wireless sensors
Up to 8 A-link sensors AP9520T/TH
Maximum number of NBPD0150 sensor pods is 6...each capable of connecting 6 wired sensors in addition to the ports available on the unit itself.
The 95051 is recommended in larger configurations. I believe it is stated that one for every 4 pods but depending on where you have it installed (interference) and how far away the pods are, you may need to use more.
Steve
(CID:113642903)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:37 PM . Last Modified: 2023-10-22 03:16 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.