Question regarding leak detection rope NBES0308 on NetBotz 570. Will alerts generated by NetBotz appliance provide the location on the rope where a leak was detected.
(CID:139694442)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:02 PM . Last Modified: 3 weeks ago
Hi Barry,
So, sadly that ability is not coded into the NetBotz appliance. You will only know that the sensor detects a leak or not. You can't see where. The only way to be more specifc in where the leak is would be to use multiple spot leaks instead of a single rope.
Thanks,
Steve
(CID:139694450)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:02 PM . Last Modified: 3 weeks ago
Hi Barry,
So, sadly that ability is not coded into the NetBotz appliance. You will only know that the sensor detects a leak or not. You can't see where. The only way to be more specifc in where the leak is would be to use multiple spot leaks instead of a single rope.
Thanks,
Steve
(CID:139694450)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:02 PM . Last Modified: 3 weeks ago
Thanks Steve, good to know. I appreciate your quick response to my question. Thanks again.
(CID:140216852)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:02 PM . Last Modified: 3 weeks ago
Put a grid of ropes on the floor ) Name the lines ABCDE and 12345. You will be able to detect the coordinate as precise as many ropes you used. i.e. A1, B2.. Battleship.
(CID:140217075)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:02 PM . Last Modified: 3 weeks ago
Hi Andrey,
That will only work if he has multiple NetBotz appliances. Each appliance only supports a single rope leak connection. You can have extensions but again, the appliance can not isolate where on the leak sensor or any extension that the leak occurred. The only way to isolate the specific location when using a single netbotz appliance is to use the spot leak.
Steve
(CID:140217084)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:02 PM . Last Modified: 3 weeks ago
Hi Steve, I'm sorry for the confusing comment. I'll try to figure out how to do a workaround.
(CID:140217163)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:02 PM . Last Modified: 2023-10-22 03:07 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.