Hi,
I want to change hostname from IP address to text naming. right know DCE showing IP on hostname column. kindly describe the procedure how to change the hostname, even don't have DNS and client IP scheme.
Ali.
(CID:105459742)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:56 PM . Last Modified: 2 weeks ago
Hi Ali!
DCE takes "Hostname" values from devices via SNMP, so only way to change it is go to the device and set it up. You can add additional property in DCE and name all devices as you want.
(CID:105459761)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:56 PM . Last Modified: 2 weeks ago
hi valentine, I put the hostname on device but it is not showing on DCE.
(CID:105459771)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:56 PM . Last Modified: 2 weeks ago
mr ,will you get any solution about this plz share ..
(CID:108828273)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:56 PM . Last Modified: 2 weeks ago
Hi Ali,
This issue is discussed in our KBase FA267667.
Issue:
Hostname field within StruxureWare Data Center Expert displays the IP address of a device and not the Hostname
Product Line:
StruxureWare Data Center Expert
Environment:
Any version
Cause:
After adding a device into StruxureWare Data Center Expert it may display the IP address within the hostname field.
Resolution:
StruxureWare Data Center Expert will put the IP address of a device into the hostname field if it is unable to look-up the IP address of the device within your DNS server to obtain the hostname. To correct the issue, please make sure that there are entries within your DNS server for the device. This may require both forward and reverse lookups. You can verify your DNS settings within StruxureWare Data Center Expert under: System > Server Administration Settings > Network Settings.
Hope this helps.
Regards
(CID:105459808)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:57 PM . Last Modified: 2023-10-31 11:04 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.