  • Failed to install EcoStruxure IT Gateway (Multi-byte Win Env)
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49249members
Join Now
242460posts
Join Now

Failed to install EcoStruxure IT Gateway (Multi-byte Win Env)

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:43 PM
0 Likes
5
113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:43 PM

Failed to install EcoStruxure IT Gateway (Multi-byte Win Env)

This question was originally posted on DCIM Support by Akihiro Yamagami on 2019-01-31


This is the successor report which I previously posted in the below. 

  • Failed to install EcoStruxure IT Gateway 1.4.3 and unable to uninstall

I reported the issue in last November, but it still happen in Ecostruxure IT Gateway 1.5.1(EcoStruxureITGateway-1.5.1.30-windows.exe).

This issue happen when installing the gateway to windows OS with Multi-byte language environment.

 

As I reported in the previous post in the above, the root cause is seemed to be the issue of installer which checks starting tomcat.

Here is the summary and corresponding logs.

  • Newly install 1.5.1.30
    Installation failed on the way.  Uninstaller is not created. So, user have to remove the resources manually.
    <console.log>, <install.log>, <bitrock_installer_988.log>

  • Upgrade install from 1.5.0.66 to 1.5.1.30
    Upgrade installation failed and rolled back to 1.5.0.66.
    <console.log>, <install.log>, <bitrock_installer.log>

 

I hope this will be fixed in the next release... 

 

Regards,

Akihiro

 

P.S.  Current work around is the below.

-----------------

To avoid the issue, the following procedure can be a workaround.

1. Before installing EcoStruxureITGateway-*.*.*.*, change the OS system locale to English(US). (See. https://java.com/en/download/help/locale.xml)

2. Install EcoStruxureITGateway-*.*.*.* (Run as administrator)

3. After the installation, change the OS system locale back to the original one. Then, restart the OS.

4. Launch the "Web Service Configuration" and add the "-Dfile.encoding=UTF8" line in Java Options. Then, Restart "EcoStruxureITGateway Server -*.*.*" service. (See. EcoStruxure IT Gateway installation in non-English Windows)

-----------------

 

 

 

(CID:138811939)

Solved! Go to Solution.

Labels
  • IT Expert
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:44 PM
0 Likes
0
113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:44 PM

Re: Failed to install EcoStruxure IT Gateway (Multi-byte Win Env)

This answer was originally posted on DCIM Support by Akihiro Yamagami on 2019-05-10


I confirmed this using Ecostruxure IT Gateway 1.6.0.39(EcoStruxureITGateway-1.6.0.39-windows.exe).

It successes to install for new installation and upgrade installation.

  • Newly install 1.6.0.39 => Success

  • Upgrade install from 1.5.2.28 to 1.6.0.39 => Success

So, this issue has been solved in Ecostruxure IT Gateway 1.6.0.39.

Thank you for your support.

 

(CID:143757196)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
5 Replies 5
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:43 PM
0 Likes
0
113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:43 PM

Re: Failed to install EcoStruxure IT Gateway (Multi-byte Win Env)

This comment was originally posted on DCIM Support by Akihiro Yamagami on 2019-02-01


FYI.

I heard the engineering team recognize the issue and is considering the fix.

(CID:138812423)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:43 PM
0 Likes
0
113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:43 PM

Re: Failed to install EcoStruxure IT Gateway (Multi-byte Win Env)

This comment was originally posted on DCIM Support by Derek Robson on 2019-02-21


Hello Akihiro Yamagami

The new 1.5.2 version of EcoStruxureITGateway that was just released should now correctly install on multibyte systems and remove the need to perform the manual workaround. 

(CID:140219828)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:43 PM
0 Likes
0
113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:43 PM

Re: Failed to install EcoStruxure IT Gateway (Multi-byte Win Env)

This comment was originally posted on DCIM Support by Akihiro Yamagami on 2019-02-25


Hello Derek,

 Thank you for your information. I tried the EcoStruxure IT Gateway 1.5.2.28 installer. (EcoStruxureITGateway-1.5.2.28-windows.exe)

For the newly installation, it successes! Thank you.

But, it failed in upgrade installation from 1.5.1.30(installed with workaround operations) to 1.5.2.28.

Here is the summary and corresponding logs.

  • Newly install 1.5.1.30 => Success! 
  • Upgrade install from 1.5.1.30 to 1.5.2.28  => Upgrade installation failed and rolled back to 1.5.1.30
    <install.log>, <bitrock_installer_9224.log>

I'm not sure it's the remaining issue of 1.5.2.28 or not.  It may be come from the issue of existing installation environment using 1.5.1.30 with work around.
But, please take care this for the next release anyway.

 

Regards,

Akihiro

(CID:140707547)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:44 PM
0 Likes
0
114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:44 PM

Re: Failed to install EcoStruxure IT Gateway (Multi-byte Win Env)

This answer was originally posted on DCIM Support by Akihiro Yamagami on 2019-05-10


I confirmed this using Ecostruxure IT Gateway 1.6.0.39(EcoStruxureITGateway-1.6.0.39-windows.exe).

It successes to install for new installation and upgrade installation.

  • Newly install 1.6.0.39 => Success

  • Upgrade install from 1.5.2.28 to 1.6.0.39 => Success

So, this issue has been solved in Ecostruxure IT Gateway 1.6.0.39.

Thank you for your support.

 

(CID:143757196)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 04:44 PM
0 Likes
0
113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 04:44 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
MateFekete
Crewman MateFekete
1
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric