EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:55 PM . Last Modified: 3 weeks ago
If i have an external battery pack attached to a UPS that is monitored in Struxureware DCE, will the UPS alert if one of the external batteries are bad?
(CID:132669551)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:55 PM . Last Modified: 3 weeks ago
Dear Todd Walters,
To answer your question, you must at least know the UPS model and the type of external batteries.
For example, Symmetra PX series UPS can connect both Schneider Electric battery cabinets (using Schneider Electric battery modules) and simply shelves with batteries (the model/type is not specified). In the first case, the brains of the UPS can identify faulty battery modules. And in the second case it is simply impossible. The maximum that can be determined by the brains of the UPS is a failure in the next self-test of the battery in general.
If you have any further questions, please ask.
With respect.
(CID:132669656)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:55 PM . Last Modified: 3 weeks ago
Dear Todd Walters,
To answer your question, you must at least know the UPS model and the type of external batteries.
For example, Symmetra PX series UPS can connect both Schneider Electric battery cabinets (using Schneider Electric battery modules) and simply shelves with batteries (the model/type is not specified). In the first case, the brains of the UPS can identify faulty battery modules. And in the second case it is simply impossible. The maximum that can be determined by the brains of the UPS is a failure in the next self-test of the battery in general.
If you have any further questions, please ask.
With respect.
(CID:132669656)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:55 PM . Last Modified: 3 weeks ago
Dear Todd Walters,
Tell us, please, did you solve your question or not?
With respect.
(CID:132670046)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:55 PM . Last Modified: 2023-10-22 02:04 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.