Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
Data Center Expert report function
EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-10-0202:58 AM
Data Center Expert report function
I have many power meters which are collection the readings form SE PM3250 meters. Some of the energy readings are added together with the virtual sensor function (total energy). I have scheduled the report creation.
My first question is that, when the DCE creates the report (which interval is the last month) it request all current data from the devices via Modbus, or it is using the readings which are collected by the DCE server? When I look such a report the time stamp line shows 23:59:59.
My second question is related with the scheduled report name. When the report file is saved it is using name like 10-01-20-070000_fXR3AGJr.txt
It is possible that the report name has the same name as the saved report name is in the DCE?
My first question is that, when the DCE creates the report (which interval is the last month) it request all current data from the devices via Modbus, or it is using the readings which are collected by the DCE server? When I look such a report the time stamp line shows 23:59:59.
Data Center Expert uses its stored values for the sensors when generating reports.
My second question is related with the scheduled report name. When the report file is saved it is using name like 10-01-20-070000_fXR3AGJr.txt It is possible that the report name has the same name as the saved report name is in the DCE?
It is not currently possible to do so. I have added this post to an enhancement request and notified product management.