Hi Team
When a try to import DWG file, the error attached appear:
Is there a solution ?
Rgds
(CID:106210211)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 04:20 AM . Last Modified: 3 weeks ago
Fabio,
The file is using unsupported elements. Supported elements can be found here: https://dcimsupport.apc.com/display/public/UAOp74/CAD+Import+Supported+Entities
Regards,
Cory
(CID:106210236)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 04:20 AM . Last Modified: 3 weeks ago
Solution is to use CAD application and remove the unsupported elements from drawing. Region and Spline could be converted to polylines. I'm not sure about 3dSolid, is this a 3D drawing?
(CID:106210259)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 04:20 AM . Last Modified: 2023-10-31 10:56 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.