This question was originally posted on DCIM Support by Mate Fekete on 2019-12-13
I wanna use Sensor Mapping in DCO-8.3.2 but system recognize the sensor in wrong type:
Sensor value is coming from DCE 7.6.0. As clearly visible the unit is Watt, but DCO allows only to convert it into Amp which would result invalid data.
If I select "Power" in sensor type drop down menu it doesn't show any sensor.
(CID:152569911)
This comment was originally posted on DCIM Support by Mate Fekete on 2019-12-13
I already have sensors which are mapped in Power type and worked well in the past:
(CID:152569920)
This answer was originally posted on DCIM Support by Greg Sterling on 2019-12-13
Hello Mate
If you return to the amps view as in the top screenshot you should be able to select the power sensors from the screenshot and delete them by clicking the delete button. If you then switch back to the power overlay in sensor mapping you should be able to click the add button to add those power sensors to the power view.
The amps view is used to convert amps readings to a watts value as DCO relies on watts for capacity planning and the power overlays in the room views.
Regards
Greg Sterling
(CID:152570184)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.