Team,
A customer tried to update a DCE server from 7.2.1 to 7.2.2. After the update the server was hanging and it was not possible to login with the client.
Fortunately we had a backup so we decided to restore the 7.2.1 server. We were able to do this without any issues, but after applying the backup to the fresh 7.2.1 it also hangs – please see attached images.
Any ideas on how we can trouble shoot this further?
Thanks,
Christian
(CID:105459394)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:50 PM . Last Modified: 3 weeks ago
Hello Christian, Prior to trying the upgrade or the restore did you run an MD5 Checksum on the downloaded files. Generally speaking issues like you're having steam from a corrupted download. Thanks Victor
(CID:105459404)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:50 PM . Last Modified: 3 weeks ago
Hi Christian,
please check if you have enough space on the DCE hard-disk. I saw this kind of issues when hard-disk was almost full.
Regards
Michael
(CID:105459419)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:50 PM . Last Modified: 3 weeks ago
Good idea! Will check disk space. Thanks 🙂
(CID:105459429)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:50 PM . Last Modified: 3 weeks ago
Hi Victor, we did not do a MD5 checksum (thanks for the reminder! 😉 but the restore itself went fine, we could log in to the client and discover devices, etc. It only hangs when we try to restore the backup file into the server.
(CID:105459428)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:50 PM . Last Modified: 3 weeks ago
Hi Christian,
Check the completion of the restore files, see if it shows complete = true from backup.properties file per below.
Also worth trying, try restoring it on a DCE 721 VM (do add the VM's hdd if your data is huge) to verify....
Regards,
Chris
(CID:105459640)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:50 PM . Last Modified: 3 weeks ago
Hi Chris, The backup.properties does say complete = true but maybe the type has something to do with the issue? It is set to type = Configuration ? Christian
(CID:105459653)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:51 PM . Last Modified: 3 weeks ago
Hi Christian,that means what you have is a config backup,not a full dc backup...:/
(CID:105459662)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:51 PM . Last Modified: 3 weeks ago
But do you need a full backup in order to restore a solution?
(CID:105459896)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:51 PM . Last Modified: 3 weeks ago
You can useDCE config backup to restore DCE config backup = DCE settings with no device data nor alarm history
(CID:105459897)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:51 PM . Last Modified: 2023-10-31 10:24 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.