Issue
Many users are unsure of the implication of the field "Interval time zone" in the Trend Log configuration window.
Product Line
EcoStruxure Building Operation
Environment
Building Operation Enterprise Server SXWSWESXX00001
Building Operation Automation Server SXWAUTSVR10001
Building Operation Automation Server Premium SXWASPXXX10001
Cause
The setting "Interval time zone" under the Trend log configuration have caused some users to believe that this setting stores trend data in either "UTC" or "Server local time"
Resolution
The trend log data is always stored in UTC time, regardless of the option selected under this setting.
This setting is intended for preventing problems with DST when the logging interval is more frequent than 1 hour.
See Interval Trend Log Properties – Basic Tab in EcoStruxure WebHelp.