  • "Not Available" in Total Compensated measurements not logging, why?
Community Menu
  • Forums
    • By Topic
        • EcoStruxure Building
          • Field Devices Forum
        • EcoStruxure Power & Grid
          • Metering & Power Quality
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Automation Forum
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
          • Motorabgangstechnik & Antriebstechnik Forum
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Solutions for Motor Management
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
          • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
        • Power Distribution NEMA
          • US Utility Forum
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure Building
        • Field Devices Forum
      • EcoStruxure Power & Grid
        • Metering & Power Quality
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Automation Forum
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
        • Motorabgangstechnik & Antriebstechnik Forum
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Solutions for Motor Management
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
        • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Power Distribution NEMA
        • US Utility Forum
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • EcoStruxure Power & Grid
          • Backstage Access Resources
        • Industrial Automation
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
          • UK&I Residential and Commercial Electrical Distribution
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
          • Solutions for eMobility
          • Digital Hospital Solutions – UK&I
        • Knowledge Center
          • Industrial Automation How-to videos
          • Digital E-books
          • Success Stories Corner
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
        • Retail
          • Solutions for eMobility
        • Retail
          • Digital Hospital Solutions – UK&I
      • EcoStruxure Power & Grid
        • Backstage Access Resources
      • Industrial Automation
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
        • UK&I Residential and Commercial Electrical Distribution
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
        • Solutions for eMobility
        • Digital Hospital Solutions – UK&I
      • Knowledge Center
        • Industrial Automation How-to videos
        • Digital E-books
        • Success Stories Corner
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
      • Retail
        • Solutions for eMobility
      • Retail
        • Digital Hospital Solutions – UK&I
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Register Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
53220members
248687posts

"Not Available" in Total Compensated measurements not logging, why?

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Metering & Power Quality
Solved
Ezequiel-PROLUX
Lieutenant Ezequiel-PROLUX
Lieutenant
‎2018-08-03 05:04 AM
0 Likes
7
181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-08-03 05:04 AM

"Not Available" in Total Compensated measurements not logging, why?

Hi all!

We are using the loss compensation framework in several ION8650 meters, and we are facing a singular situation that we want to understand better.

We have the document "Transformer / line loss calculations" and use the "Transformer loss only" section. The data from the test sheet is below:

 

 

So when we verify the readings in NORMAL mode it show as "not available", like below:

 

 

but if we verify it in TEST mode, the values are shown, like below:

 

 

BUT, if we put those parameters in an ION8500 meter, it shows values in kW total compensated but shows "not available" only in kVAR total compensated. This behavior occurs in both normal or test mode verification. The big problem is that when it shows "not available", it stops logging the data in revenue log, as shown below in kVARh comp d int:

 

 

Thanks in advance!!!!!

Labels
  • ION Setup
Tags (2)
  • Tags:
  • ion meter
  • power_losses
Share
Reply

Accepted Solutions
Robert_Lee
Captain Robert_Lee Captain
Captain
‎2018-08-09 09:26 AM
0 Likes
1
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-08-09 09:26 AM

Re: "Not Available" in Total Compensated measurements not logging, why?

Each default Setup Assistant is matched up with a corresponding default device template.  If you customize either, then some type of customization is required.

Looking at the factory 8650 Setup Assistant, it seems for Normal mode, its attempting to show the 2 output registers from the Arithmetic 24 module:

;kW Compensation

Tab1Reg1Tab4Group3Display6=0,0x4A8F

Tab1Reg1Tab4Group3Display6Label=Total Compensated

;kVAR Compensation

Tab1Reg1Tab4Group4Display6=0,0x4AA1

Tab1Reg1Tab4Group4Display6Label=Total Compensated

Verify the formulas and inputs are set properly:

Hold down <Shift> when clicking on the "Inputs" tab and it will show present values (make sure none are N/A).

This is likely either an incorrect Setup Assistant reference (likely caused by framework customization) or some issue within the device's template configuration (either inputs or setup register values).

See Answer In Context

Share
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard
‎2020-05-04 12:10 PM
0 Likes
1
137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-05-04 12:10 PM

Re: "Not Available" in Total Compensated measurements not logging, why?

Hello @Ezequiel-PROLUX 

 

Did you still need help with this?  Regarding the N/A, you are correct that VA rated * Imp has to be larger than LWCu in order to calculate the LVCu.

 

As for showing values in test mode vs normal vs Advanced I will need to know a few more details.

 

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
7 Replies 7
Ezequiel-PROLUX
Lieutenant Ezequiel-PROLUX
Lieutenant
‎2018-08-08 08:14 AM
0 Likes
0
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-08-08 08:14 AM

Re: "Not Available" in Total Compensated measurements not logging, why?

Any suggestions??

Share
Reply
Robert_Lee
Captain Robert_Lee Captain
Captain
‎2018-08-09 09:26 AM
0 Likes
1
151
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-08-09 09:26 AM

Re: "Not Available" in Total Compensated measurements not logging, why?

Each default Setup Assistant is matched up with a corresponding default device template.  If you customize either, then some type of customization is required.

Looking at the factory 8650 Setup Assistant, it seems for Normal mode, its attempting to show the 2 output registers from the Arithmetic 24 module:

;kW Compensation

Tab1Reg1Tab4Group3Display6=0,0x4A8F

Tab1Reg1Tab4Group3Display6Label=Total Compensated

;kVAR Compensation

Tab1Reg1Tab4Group4Display6=0,0x4AA1

Tab1Reg1Tab4Group4Display6Label=Total Compensated

Verify the formulas and inputs are set properly:

Hold down <Shift> when clicking on the "Inputs" tab and it will show present values (make sure none are N/A).

This is likely either an incorrect Setup Assistant reference (likely caused by framework customization) or some issue within the device's template configuration (either inputs or setup register values).

See Answer In Context

Share
Reply
Ezequiel-PROLUX
Lieutenant Ezequiel-PROLUX
Lieutenant
‎2018-08-15 01:17 PM
0 Likes
0
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-08-15 01:17 PM

Re: "Not Available" in Total Compensated measurements not logging, why?

Hi Robert!

Thanks!

For the ION8650 I am using the offline template, ION8650AV403_Offlinemeter.exe

I was digging around to find what calculation was throwing the N/A, and I found it in the arithmetic 8 - W+VARCuLoss1.

I am following the document 70072-0153-08 in the "transformer loss only" section, that says to leave kVA rated in 0.

But if I do so, the values are like follow:

Using like 150kVA for the kVA rated and keeping other values, the result is like follow:

the setup registers are the same.

The test sheet used this data:

I noticed that we need errorflag = 1 for this function work, but the S4² is much greater than S3*1000*S5/100, so the SQRT is negative.

Is probably a limit of losses for compensation to work?

Share
Reply
Ezequiel-PROLUX
Lieutenant Ezequiel-PROLUX
Lieutenant
‎2018-08-15 01:58 PM
0 Likes
3
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-08-15 01:58 PM

Re: "Not Available" in Total Compensated measurements not logging, why?

I noticed that we need to have:

kVA rated*%Imp*10 > LWCu Test

But we have a top limit for %Imp and LWCu Test that are not necessary related as the calculation require.

There is a regulation followed by Schneider on this topic?

Share
Reply
Ezequiel-PROLUX
Lieutenant Ezequiel-PROLUX
Lieutenant
‎2018-08-20 04:32 AM
0 Likes
0
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-08-20 04:32 AM

Re: "Not Available" in Total Compensated measurements not logging, why?

One thing that is very curious, is that if I look in TEST  MODE it show values for the "Total Compensated" in both kW and kVAR, but in NORMAL MODE or in Advanced Mode for ION Setup it shows N/A. Keeping those test sheet values that we know aren't OK.

Share
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard
‎2020-05-04 12:10 PM
0 Likes
1
138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-05-04 12:10 PM

Re: "Not Available" in Total Compensated measurements not logging, why?

Hello @Ezequiel-PROLUX 

 

Did you still need help with this?  Regarding the N/A, you are correct that VA rated * Imp has to be larger than LWCu in order to calculate the LVCu.

 

As for showing values in test mode vs normal vs Advanced I will need to know a few more details.

 

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Share
Reply
Ezequiel-PROLUX
Lieutenant Ezequiel-PROLUX
Lieutenant
‎2020-05-04 02:05 PM
0 Likes
0
133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-05-04 02:05 PM

Re: "Not Available" in Total Compensated measurements not logging, why?

Hi Charles.

 

No, later I founded a guide to configure losses on ION8650 and the formula was there too.

With Lee's help I could recognize that the input data was wrong.

Thanks.

 

Share
Reply
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
144
Robert_Lee
Captain Robert_Lee Captain
56
Ramasamy_N
Commander Ramasamy_N Commander
41
DanL
Lt. Commander DanL Lt. Commander
31
Nedjma
Nedjma Community Alumni (Retired)
24
Daniel_Brandao
Lt. Commander Daniel_Brandao Lt. Commander
17
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2021, Schneider Electric