The "HDPM6000 CT Type Table" zip file attached to this post contains an updated HDPM6000 CT Type table file (CSV) that uses METSE reference names for most CTs available for the HDPM6000 platform. This approach should simply the task of assigning CTs to branch channels, allowing users to select CT names that match the METSE reference name printed on the CT label.
A HDPM6000 head unit maintains a CT Type table with calibration data for CTs that are compatible with HDPM6000 systems. Each CT entry in the table is given a unique name, CT factor (magnitude) value, and PHCAL (phase shift) value. The CTs defined in the CT Type table can be selected when configuring CTs connected to the head unit and branch circuit module channels within the Channel Cfg tab of the web user interface on the head meter. CT Type table files (CSV format) are used to add new CT entries to the CT Type table maintained by a HDPM head unit.
NOTE: Uploading a CT Type table file to a HDPM head unit does not delete existing entries in the CT Type table maintained by the head unit. Modifications to existing CT parameters in the table will be applied and new entries will be added.
The HDPM6000 Manager software utility is used to upload CT Type table files to a head unit. See the "HDPM6000 Manager" section in the HDPM6000 Head Unit Installation Guide for information about uploading a CT Type table to a head unit. HDPM6000 Manager is bundled with system firmware that is available in the Software and Firmware section of the HDPM6000 section of the se.com web site.
NOTE: HDPM6000 head unit firmware v62.7 and above supports up to 500 CT Type table entries. Head units with previous firmware versions support fewer table entries and may display an error if a CT Type table file upload adds new entries that exceed the table limit.
Link copied. Please paste this link to share this article on your social media post.
Updated the CT Type Table from v1.4 to v1.5. Changes introduced in v1.5 include: