Hello,
Can anyone tested and used the PM5560 for the concurrent connections on both RS485 port and Ethernet port?
We are having a request to use this way to segregate the meter reading from two "separate" networks ( PME and non-SE BMS).
Thank you in advance.
Tun
Link copied. Please paste this link to share this article on your social media post.
Hi @Tun
The PM5560 has the capability to communicate simultaneously via serial RS485 and Ethernet ports with two different systems through Modbus.
Best Regards,
-Mehran
L3 Expert Technical Support Specialist
Link copied. Please paste this link to share this article on your social media post.
Hi @Tun
The PM5560 has the capability to communicate simultaneously via serial RS485 and Ethernet ports with two different systems through Modbus.
Best Regards,
-Mehran
L3 Expert Technical Support Specialist
Link copied. Please paste this link to share this article on your social media post.
Thank you, Mehran