APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:59 PM . Last Modified: 2024-03-22 04:30 AM
I foolishly connected my battery reversed to my BK605MC. A spark later and the UPS is completely dead.
I see two paralleled 40 amp fuses between battery+ and the board but they are both good, and the unit breaker is set in/on. Next to both battery leads are board traces that say "F 5 amp" but they are copper strips on the circuit board and good anyway.
Any advice where to start? I know my way around with a schematic but Im blind... Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:59 PM . Last Modified: 2024-03-22 04:30 AM
Let me give APC a design idea - FUSE the DC outputs to the battery! Whats that cost - 30 cents?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:59 PM . Last Modified: 2024-03-22 04:30 AM
Very enlightening post from KVAr, thank you for that!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:59 PM . Last Modified: 2024-03-22 04:30 AM
unfortunately, APC cannot provide internal schematics as they are proprietary. i am not sure if anyone around here has any general useful information though..
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:59 PM . Last Modified: 2024-03-22 04:30 AM
Let me give APC a design idea - FUSE the DC outputs to the battery! Whats that cost - 30 cents?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:59 PM . Last Modified: 2024-03-22 04:30 AM
Hi, am not sure that would provide your intended protection really.
It only takes 0.65V reverse to destroy a solid state junction {which is what may have happened} and providing some form of polarity protection is going to lead to DC losses along the way.
An alternative could be polarised connectors which some of the larger units have, I guess where the unit you are dealing with is using spade terminals.
Good luck and sorry I couldn't be more helpful.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:59 PM . Last Modified: 2024-03-22 04:30 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:59 PM . Last Modified: 2024-03-22 04:30 AM
Very enlightening post from KVAr, thank you for that!
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.