Hello.
So I've purchased "Back-UPS Pro 1500" and here's my story.
Firstly I placed it under a dedicated circuit breaker (rated to allow up to 6 Amps), but I noticed that it tripped pretty much every single time after my UPS had been left off for a longer period (a night is long enough). It tripped even with no computers connected and only when powering up the UPS (meaning I could restart the circuit breaker and everything was smooth since then).
So yeah, I thought 6 Amps may be too pesky, therefore I got it replaced with 10 Amps (Hager B10 MB110) and... nothing has changed!
Then I borrowed a power meter (or whatever it's called in English) and today in the morning evaluated that tripping occurred within circuit containing less than 3 Amps.
It might also be worth mentioning that whole room is protected by another 16 Amps circuit breaker which has never tripped at all.
How should I properly choose a circuit breaker? Maybe you can even mention a few specific models (I'm not sure if this is a good idea since I expect many of you live in USA and I live in Europe)?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:13 PM . Last Modified: 2024-03-20 03:09 AM
Well, I'm not too good at these things.
However, my country uses the three-wire system (phase wire, neutral wire, ground wire) and since this present circuit breaker makes use of phase wire only, I believe it is not GFCI (assuming it should have something to do with ground wire otherwise) 😄
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:13 PM . Last Modified: 2024-03-20 03:09 AM
what type of breaker is it? is it a GFCI breaker?
http://nam-en.apc.com/app/answers/detail/a_id/1344
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:13 PM . Last Modified: 2024-03-20 03:09 AM
Well, I'm not too good at these things.
However, my country uses the three-wire system (phase wire, neutral wire, ground wire) and since this present circuit breaker makes use of phase wire only, I believe it is not GFCI (assuming it should have something to do with ground wire otherwise) 😄