APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:24 PM . Last Modified: 2024-03-20 12:37 AM
Hi,
We recently moved from the Infrastruxure Central (ISX) physical appliance to StruxureWare Data Center Expert (SDCE) version 7.2.1 (VM). Is there a way I can import devices previously monitored by ISX to new SDCE?
I performed a FULL backup via ISX but when I attempt to restore a backup via SDCE, the location shows up empty. Are there any steps I need to follow to make this work?
Thank you.
Bhaskar
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:24 PM . Last Modified: 2024-03-20 12:37 AM
Hi Bhaskar,
You need to be on the same version to import the backup to DCE. If you do not want to lose historical data, you need to create a backup on the physical machine but you need to be on version 7.2.1. Then you can import the backup from the physical machine to the VM. Although, once you have unlocked the VM using the activation code, you can do a discovery on the VM, and it will discover the devices on your network.
Regards,
B
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:24 PM . Last Modified: 2024-03-20 12:37 AM
Hi Bhaskar,
You need to be on the same version to import the backup to DCE. If you do not want to lose historical data, you need to create a backup on the physical machine but you need to be on version 7.2.1. Then you can import the backup from the physical machine to the VM. Although, once you have unlocked the VM using the activation code, you can do a discovery on the VM, and it will discover the devices on your network.
Regards,
B
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.