APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:06 AM . Last Modified: 2024-03-22 12:57 AM
Hi,
we have UPS 5000 with AP 9631. I am trying to configure network connection for UPS ...
First try:
I tried to setup network parameters on NMC throug "Device IP Configuration Wizard".
The message was "... ip address is in use ..."
IP is not in use.
Second try:
Use serial cable and connect UPS to machine.
Hyper Terminal connection parameters are (from link: http://nam-en.apc.com/app/answers/detail/a_id/3061😞
I have cable 940 1525 A. Connect it to Universal I/O on UPS and Serial on machine.
Properties of hyper connection:
9600 bps, 8 data bits, no parity, 1 stop bit, and no flow control.
but there is no answer ....
Once with IBM UPS 3000XHV it passed with:
2400 bits per second, flow control Xon/Xof, and disable advanced option on COM properties- "Use Fifo Buffers"
pls for any information I would appreciated it ...
thank you for your time,
Indira
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:06 AM . Last Modified: 2024-03-22 12:57 AM
Hi,
we have UPS 5000 with AP 9631. I am trying to configure network connection for UPS ...
First try:
I tried to setup network parameters on NMC throug "Device IP Configuration Wizard".
The message was "... ip address is in use ..."
IP is not in use.
Second try:
Use serial cable and connect UPS to machine.
Hyper Terminal connection parameters are (from link: http://nam-en.apc.com/app/answers/detail/a_id/3061😞
I have cable 940 1525 A. Connect it to Universal I/O on UPS and Serial on machine.
Properties of hyper connection:
9600 bps, 8 data bits, no parity, 1 stop bit, and no flow control.
but there is no answer ....
Once with IBM UPS 3000XHV it passed with:
2400 bits per second, flow control Xon/Xof, and disable advanced option on COM properties- "Use Fifo Buffers"
pls for any information I would appreciated it ...
thank you for your time,
Indira
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:06 AM . Last Modified: 2024-03-22 12:57 AM
Hi Indira,
What is the exact model number of your UPS? Also, the AP9631 card comes with another kind of cable it is a serial to TRS (tip-ring-sleeve) and the part number is 940-0299. You can use this cable to access HyperTerminal and the settings would be 9600-8-None-1-No Flow Control. You can also use the 940-0024 or 940-1524 cables and the terminal emulation settings would be 2400-8-None-1-No Flow Control.
JonPro
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:06 AM . Last Modified: 2024-03-22 12:57 AM
Sorry, double post.
Message was edited by: JonPro
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:06 AM . Last Modified: 2024-03-22 12:57 AM
thank you JonPro, very, very much.
I found cable 940-0299 (somewhere in box 🙂 ), setup connection as you said, and it works !
I hope that everythin else will be ok.
thank you for you time,
Keli
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:06 AM . Last Modified: 2024-03-22 12:57 AM
Hi,
we have UPS 5000 with AP 9631. I am trying to configure network connection for UPS ...
First try:
I tried to setup network parameters on NMC throug "Device IP Configuration Wizard".
The message was "... ip address is in use ..."
IP is not in use.
Second try:
Use serial cable and connect UPS to machine.
Hyper Terminal connection parameters are (from link: http://nam-en.apc.com/app/answers/detail/a_id/3061😞
I have cable 940 1525 A. Connect it to Universal I/O on UPS and Serial on machine.
Properties of hyper connection:
9600 bps, 8 data bits, no parity, 1 stop bit, and no flow control.
but there is no answer ....
Once with IBM UPS 3000XHV it passed with:
2400 bits per second, flow control Xon/Xof, and disable advanced option on COM properties- "Use Fifo Buffers"
pls for any information I would appreciated it ...
thank you for your time,
Indira
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.