APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:09 PM . Last Modified: 2024-03-21 01:00 AM
Hello,
We have:
APC Smart-UPS,2700 Watts /3000 VA,Input 230V /Output 230V
we also have:
a very important-consumer device 230V 12A
We should very much like to know if our UPS is able to provide enough power to the consumer device,
from **JUST ONE RECEPTACLE** ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:09 PM . Last Modified: 2024-03-21 12:59 AM
I believe these are the general ratings for both C13 and C19 as I wasn't sure what outlet you were plugging it into. Depending on what region you're located in, these would apply to the outlet itself.
IEC-320-C13: 12 A; IEC-320-C19: 16 A UL (derated)
IEC-320-C13: 10 A; IEC-320-C19: 16 A VDE
IEC-320-C13: 15 A; IEC-320-C19: 20 A PSE
I had thought at 230V, C13's could provide 10A max where as with 208 and 200V they are derated to 12A.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:09 PM . Last Modified: 2024-03-21 01:00 AM
You're exactly right!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:09 PM . Last Modified: 2024-03-21 12:59 AM
i wish you a million points and a million years of fruitful professional activity.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:09 PM . Last Modified: 2024-03-21 12:59 AM
Hello,
We have:
APC Smart-UPS,2700 Watts /3000 VA,Input 230V /Output 230V
we also have:
a very important-consumer device 230V 12A
We should very much like to know if our UPS is able to provide enough power to the consumer device,
from **JUST ONE RECEPTACLE** ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:09 PM . Last Modified: 2024-03-21 12:59 AM
I believe these are the general ratings for both C13 and C19 as I wasn't sure what outlet you were plugging it into. Depending on what region you're located in, these would apply to the outlet itself.
IEC-320-C13: 12 A; IEC-320-C19: 16 A UL (derated)
IEC-320-C13: 10 A; IEC-320-C19: 16 A VDE
IEC-320-C13: 15 A; IEC-320-C19: 20 A PSE
I had thought at 230V, C13's could provide 10A max where as with 208 and 200V they are derated to 12A.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.