Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
BR24BPG Manufacturing issues
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-2910:35 PM. Last Modified: 2024-03-1911:38 PM
BR24BPG Manufacturing issues
I have recently discovered a disturbing series of defects to this model battery pack often used as a replacement for packs in a number of APC UPS products (in my case the BR1500G). This defect causes flaky performance and ERROR 02 over time (about two years) during normal operation of the UPS due, I feel, to bad manufacture and mis-assembly and bad QA, in cases of OEM.
The error could occur easily enough, resulting in premature failure or what may even seem to be "normal out-of warranty failure" of the UPS as it was described to me by the APC Support department. This is especially true when you need the device to work reliably - when a power failure does occur. From the front panel you can catch this failure in advance if you observe the lower bar of the LCD display go to no bars of battery voltage all by itself. Of course, if your unit is out of warranty you cannot expect any help from Support in diagnosing this condition. They certainly offered me no advice other than replace the battery pack or replace the unit. If I had replaced the individual batteries as some have said elsewhere, I be in the same pickle because the batteries were fine (though somewhat aged).
In the above case, you should keep a sharp eye out for the protrusion of the pins on the original or any purchased replacement battery packs, especially those purchased on Amazon. I received two packs which were BOTH defective on receipt. APC only exchanged one of them for me, so I took one defective BR24BPG unit apart to find the trouble. What I found may surprise you, it certainly did for me!
Initially, it looked like both pin their slide in pack which marries TWO 12VDC 9AH batteries together to mount in the device did not protrude outward in the connector to contact the mating connectors in the UPS housing assembly.
I made a go-no-go gauge to measure which one worked and which one didn't, in either of my two BR-1500G's. It is actually a pretty bad design to have the whole pack held in by a piece of plastic against the force of gravity of a 10# weight - the two batteries inside the UPS pushed up to their connection in a plastic case. The two replacements failed miserably and the OEM battery was barely good enough to continue to work. The replacement received from APC under warranty however worked fine, so I used this as a standard for the good amount of protrusion. I found problems with three out of four packs inspected - to include loose, unglued pins, pins glued in at the wrong protrusion.
The key to the mystery of failing performance of the OEM unit over time and the replacements however is what I found when disassembling a known bad pack. This 'coupling plate' between the two batteries has three wires - two the connect the pins on the plate and one jumper wire - with four push-on connections at the batteries. The connectors on the pack utilize two push in pins that are typically glued into their slots on the plate. These pins in my dis-assembled defective plate, simply fell out when I held the plate up, so they were never glued in and more importantly were able to back themselves out over time!! So, a drop of glue was the key to the defect of the original pack.
Armed with this knowledge and some capability and some glue or observation by you, the user you can at least detect the problem. Good luck getting APC to fix all the old, out-of warranty units.