I have a BP 1000 serving my workstation computer, monitors, and speakers.
Occasionally the UPS chirps like a cricket for about 15 seconds and then it goes silent. It still operates and the computer runs uninterrupted during these episodes. I have not looked at the LEDs during this chirping.
Lately, the UPS shuts off without warning, and the computer turns off as if you pulled it's plug from the outlet. Then the UPS turns back on.
I have tested the UPS by unplugging the computer and all peripherals from it, plugging in a lamp, and pulling the UPS is power cord from the wall outlet. When this is done the battery LED illuminates. When plugged back into the wall outlet, the UPS returns to normal operating mode.
I have replaced its battery several years ago with an APC replacement model. But if the battery was bad again, wouldn't the "replace battery" LED be illuminated?
It has been years since we last lost power, and the UPS performed as expected. Occasionally we have what I would describe as brownouts, where the lights in the building quickly flash on and off. When this occurs the UPS humms briefly and then returns to normal mode.
The UPS is connected to my computer with a serial cable. In the power options properties window the manufacturer is set to American Power Conversion and the model is set to badk-ups. Its status is AC Power.
Does anyone know why the UPS occasionally shuts off without warning?
Message was edited by: ctc
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:02 PM . Last Modified: 2024-03-22 04:26 AM
I completely agree with syn on this one. Definitely sounds like a combination of old/weak battery and a relatively high load.
Time for a new battery. 5 years battery life is excellent, so don't ignore the most obvious possibility that the battery requires replacement.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:02 PM . Last Modified: 2024-03-22 04:27 AM
Hello, here are some more questions to try and help determine what is going on here.
When the UPS shuts off does it make any kind of alarm or warning before doing so?
Do you know how old the battery is?
Do you know if the unit has/can pass a self test?
What type of chirping do you hear, could you give an example of the pattern, if any?
Are you using any shutdown software that might be initiating a shutdown from a parameter that the UPS might be meeting?
It could be that the UPS battery is very weak, if you say its been in the unit for a few years, and is failing during a ST which is dropping your load. It also might be from a power issue, dirty power, low or high voltage, etc.
Let us know what you find
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:02 PM . Last Modified: 2024-03-22 04:27 AM
Thanks for your help.
When the UPS shuts off does it make any kind of alarm or warning before doing so?No
Do you know how old the battery is? *5 yrs. + or -*
Do you know if the unit has/can pass a self test?I believe that the UPS performs and passes a self test each time it is turned on, which I do shortly after it shuts off.
What type of chirping do you hear, could you give an example of the pattern, if any?It sounds like a continuous cricket for about 15 sec.
Are you using any shutdown software that might be initiating a shutdown from a parameter that the UPS might be meeting?No. Windows xp power management only.
It could be that the UPS battery is very weakIf that was the case shouldn't the "replace battery" LED be illuminated?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:02 PM . Last Modified: 2024-03-22 04:27 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:02 PM . Last Modified: 2024-03-22 04:26 AM
I completely agree with syn on this one. Definitely sounds like a combination of old/weak battery and a relatively high load.
Time for a new battery. 5 years battery life is excellent, so don't ignore the most obvious possibility that the battery requires replacement.