Enhanced Mode is for b3 controllers only. Therefore, there should be a recommendation to change the setting for the following conditions:
If MSTP Comm Port has all b3 controllers, then Enhanced Mode should be TRUE.
If there are no b3 controllers on that MSTP Comm Port, then Enhanced Mode should be FALSE.
If there is a mix of b3 and other BACnet devices, then either position could improve or worsen communications, so it does not need to be included in a recommendation.