APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:31 AM . Last Modified: 2024-03-12 03:00 AM
have a su2200net that during self-test when it goes to battery it shuts down. Which the defect Batteries are good
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:31 AM . Last Modified: 2024-03-12 02:59 AM
Hello. Can I ask how you know the batteries are good? They might report a good voltage but are unable to support a load over time. How old are they?
And when you say "it shutsdown" - do you mean the UPS itself, the load you may have attached to the UPS, or both?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:31 AM . Last Modified: 2024-03-12 03:00 AM
What other equipment did you test it in? A UPS? With the same load? And can you provide answers to my other questions?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:31 AM . Last Modified: 2024-03-12 03:00 AM
You should test the batteries and UPS with a light load. I suggest attaching a lamp to the unit and then unplug the UPS from the AC source. If the lamp stays lit then the batteries are fine. Next I would plug the UPS back into the AC source and with the lamp powered on run a selftest. If the lamp powers down then there is an issue with the UPS and it should be replaced.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:31 AM . Last Modified: 2024-03-12 03:00 AM
have a su2200net that during self-test when it goes to battery it shuts down. Which the defect Batteries are good
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:31 AM . Last Modified: 2024-03-12 02:59 AM
Hello. Can I ask how you know the batteries are good? They might report a good voltage but are unable to support a load over time. How old are they?
And when you say "it shutsdown" - do you mean the UPS itself, the load you may have attached to the UPS, or both?
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.