Hello,
I'm trying to configure a couple of SYA16K16Ps that have 2 SYPD3 in them.
We're in the US, and are currently using NEMA 5-15 cables @ 120V to the servers and storage units.
I want to now change over to 208V on all the servers.
I've looked around, and I see that I can use the APC AP9566 PDU with the SYPD3.
i.e SYPD3's L6-20R to AP9566's L6-20P .
However, the AP9566 has (12) IEC 320 C13 on the output side.
Would I just need an IEC passthru cable to connect power to the servers?
Can't even seem to be able to find those.
Or am I missing something here?
If so how are people here running their standard issue US devices @ 208?
Message was edited by: a_0_0
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:50 AM . Last Modified: 2024-03-08 04:02 AM
what type of power plugs do your servers have?
I believe that they should come with power cables that are something like C13 (PDU) to C14 (server end)..?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:50 AM . Last Modified: 2024-03-08 04:02 AM
oh ok i understand.
glad you found what you needed!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:50 AM . Last Modified: 2024-03-08 04:02 AM
what type of power plugs do your servers have?
I believe that they should come with power cables that are something like C13 (PDU) to C14 (server end)..?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:50 AM . Last Modified: 2024-03-08 04:01 AM
The servers have 320 C14 chassis sockets on them.
We've been using your basic C13 to NEMA 5-15P.
In any case, I think I've found the cables I'm looking for.
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9870
We have a few of this cable already.
The information was just not as readily accessible on APC's website.
i.e. it wasn't listed as an option for the Symmetra LX .
Thanks for the reply.
.