APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:09 AM . Last Modified: 2024-03-05 01:44 AM
I have a quick question on which version of PCNS I should download. I've seen the compatibility list. I have a VMware ESXi 5.1 server which is compatible with PCNS 3.1. I will be running the PCNS in the VMa 5.1 guest on this host.
My concern is that one of the Guest machines on the Host is a Windows SBS 2011 Server, which the compatibility list recommends to use PCNS 3.0.1 with.
Since PCNS will actually be running on the VMa 5.1 guest, am I OK using PCNS 3.1? Will it cause any problems trying to shut down the SBS 2011 server on power loss?
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:09 AM . Last Modified: 2024-03-05 01:44 AM
The ESXi host will be doing the shutting down of the VMs, right? For what you plan to configurr? That is what most users do rather than installing PCNS on each VM. So, after the VMA issues the RCLI command to turn the host off, the SBS 2011 server would shutdown like if ESXi commanded it to upon your request manually. You should only need to worry about PCNS on the VMA and that compatibility there - which you already verified.
Bill P. - I didn't miss anything did I?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:09 AM . Last Modified: 2024-03-05 01:44 AM
The ESXi host will be doing the shutting down of the VMs, right? For what you plan to configurr? That is what most users do rather than installing PCNS on each VM. So, after the VMA issues the RCLI command to turn the host off, the SBS 2011 server would shutdown like if ESXi commanded it to upon your request manually. You should only need to worry about PCNS on the VMA and that compatibility there - which you already verified.
Bill P. - I didn't miss anything did I?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:09 AM . Last Modified: 2024-03-05 01:44 AM
Hello,
Just an added note. As of PCNS 3.1, we have a virtual appliance available for download. This would be easier to deploy than the VMA, as you have to download VMA and then install PCNS on that VMA. If you search for the code SFPCNS31-V, you can download the virtual appliance. To gracefully shutdown the VM's, you need to make sure that VMWare tools is installed on each virtual machine.
Regards,
B
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:09 AM . Last Modified: 2024-03-05 01:43 AM
Thanks for the great information. Sorry I can't mark both as correct! I will give that virtual appliance a try.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.