Personnel Template Error: Error in datagrid DataGridViewComboBoxCell value is not valid.

Personnel Template Error: Error in datagrid DataGridViewComboBoxCell value is not valid.

Issue

In the Personnel Manager, the template field shows an error: "Error in datagrid DataGridViewComboBoxCell value is not valid."

Product Line

Andover Continuum

Environment

  • Continuum 1.93 and below
  • Personnel Templates

Cause

Error occurs while attaching the Personnel Templates to a personnel from the Personnel Manager. The selected Template is not in the default template folder (Personnel Templates).

Note: It is still possible to attach the templates through the method of CSV importing/exporting of personnel.

If the Templates are created under the "Templates" Folder, this error occurs. The Personnel Templates should be created under "Templates\Personnel Templates".

Resolution

  1. Select all the Personnel Templates and move them (Right Click + Drag) to "Personnel Templates" Folder.
  2. It will give you an option to "Move Here". See the below screen shot.
  3. Click on "Move Here" to complete moving the Personnel Templates.

Alternatively:

Go to the "Properties" of the Template, then change the path of the Owner.