APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:56 AM . Last Modified: 2024-03-27 01:23 AM
Hi everyone, I just bought the APC BX1100LI-MS Battery Backup model. After I read the manual instruction its say that it is recommended to plug the UPS directly into the wall outlet. However, since the wall outlet is quite far from my PC location, I use the power strip. So I want to ask, it is actually fine if I plug the UPS into power strip? Thx before.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:56 AM . Last Modified: 2024-03-27 01:23 AM
Hi Jack,
Schneider Electric recommends against the use of surge protectors, power strips, or extension cords being used in conjunction with a UPS. Plugging your UPS into a surge protector or power strip my cause the UPS to go to battery more often than it would if it was plugged directly into the wall outlet and it may also compromise the ground connection that the UPS needs to properly protect against spikes and surges. In many cases this may also void the Equipment Protection Policy (EPP) of your UPS.
Nicole
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:56 AM . Last Modified: 2024-03-27 01:23 AM
Jack,
It should be OK, as long as you plug your PC to your APC UPS and you don't have a lot of the other power strip outlets used.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:56 AM . Last Modified: 2024-03-27 01:23 AM
Hi Jack,
Schneider Electric recommends against the use of surge protectors, power strips, or extension cords being used in conjunction with a UPS. Plugging your UPS into a surge protector or power strip my cause the UPS to go to battery more often than it would if it was plugged directly into the wall outlet and it may also compromise the ground connection that the UPS needs to properly protect against spikes and surges. In many cases this may also void the Equipment Protection Policy (EPP) of your UPS.
Nicole
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:56 AM . Last Modified: 2024-03-27 01:23 AM
Thx everyone for the answers.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.