APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-15 11:33 PM . Last Modified: 2023-01-15 11:34 PM
Dear community,
I’m currently in the process of installing PCNS in the below described environment, but cannot find any information on the “Application Note 180” regarding the sequence that would be triggered by a power event, as our setup does not correspond to any scenario on that note.
We have 2 sites, A and B, that are actually 2 server rooms in the same building. Each of those sites is protected by a single UPS (a Smart-UPS X 3000 in site A and a Smart-UPS 3000 in site B). We have 4 hosts with local storage on site A and 3 on site B. There is no SAN or storage array of any kind, the VM’s run on the local storage of the hosts. The PCNS VM is running in site B, as is the vCenter VM, and we have vSphere STD licenses.
What would be the behaviour of the PCNS and the sequence triggered in those cases :
Thanks in advance for your help
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-19 12:29 PM
To accomplish this, you should install two instances of PCNS. One on site A and one on site B. They both can be configured with the same vCenter. When selecting which hosts to power off you would only select the hosts per site.
In the screenshot above site one is protect by the PCNS instance. Site two is not, but it has its own instance of PCNS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-19 12:29 PM
To accomplish this, you should install two instances of PCNS. One on site A and one on site B. They both can be configured with the same vCenter. When selecting which hosts to power off you would only select the hosts per site.
In the screenshot above site one is protect by the PCNS instance. Site two is not, but it has its own instance of PCNS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-23 12:26 AM
Hello BillP,
Many thanks for your efficiency ! Your answer has been quick and precise. I'll setup a second PCNS instance in the coming days. Have a nice week 🙂
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.