Help repairing my HI - 800 SQ ups inverter ...
The inverter is charging the battery properly at 13.60 volts..
But when the line goes off it stays on for 2 - 3 minuits and turns off...
The FAULT LED, ON BATTERY and ON MAINS LEDs keps flashing...
Even when the inverter is on mains and I open the battery terminals the inverter does not show the fault..
Where as if the battery terminal is opened the FAULT led should flash and the inverter should beep...
I have attached the manual of the inverter below..
Message was edited by: nemo4all
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:11 AM . Last Modified: 2024-03-21 05:03 AM
What Is The Serial Number Of The Unit And When You Last Replaced The Batteries
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:11 AM . Last Modified: 2024-03-21 05:03 AM
What Is The Serial Number Of The Unit And When You Last Replaced The Batteries
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:11 AM . Last Modified: 2024-03-21 05:03 AM
The serial number of the product is BB0950014478
The battery is just 1 year old...
I have another good APC Hi800SQ inverter.. When I connect that with this battery it runs well
SO there is not a battery problem..
I have charged the battery with an external charger and have tested the voltage.. It shows 13.92 volts.. I have tested the battery with a load too... Every thing is fine with the battery...
It is the inverter problem..