Can I maxout my UPS from time to time?

Solved
BillP
Administrator Administrator
Administrator
0 Likes
5
143

Can I maxout my UPS from time to time?

This question was originally posted by Davide on APC forums on 1/31/2016


Hi,
sometimes the load of my PC goes up to 870W, it is rare but it may happen.
When pushing the graphics cards hard the average is 800-820W.

I'm using a BackUPS PRO 1500VA 865W.

Is this a problem for the peripherals or the UPS?

What happen if I put a load of 870 or 880W on my UPS?
Can I damage it?
Can the UPS damage the attached peripherals if I put 880W on it?

Thanks.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
143

Re: Can I maxout my UPS from time to time?

This reply was originally posted by Bill on APC forums on 2/1/2016


Hi,

Any Smart-UPS 1500, 2200, 3000 can be used in the home but you need to be aware of the power requirements. Any unit that is larger than 1500 KVA will require a circuit larger than the standard 15 amp house hold circuit (U.S. standards). The larger the load placed on the UPS the larger the load that is placed on the home circuit. 

Example: SMT2200i 230 V requires input connector IEC-320 C20, Schuko CEE 7 / EU1-16P, British BS1363A

Max Configurable Power (Watts) 1.98 KWatts / 2.2 kVA

See Answer In Context

5 Replies 5
UnexpectedBill_apc
Captain
Captain
0 Likes
0
143

Re: Can I maxout my UPS from time to time?

This was originally posted on APC forums on 2/1/2016


If overloaded while running from the battery, the UPS will shut down. Damage to anything is unlikely. (You might lose any unsaved work, or have to run a verification routine on your file system if the UPS shuts down suddenly.)

It's best to keep your UPS loaded to within no more than 50-60% of its output capacity. That way you have room for future expansion, and you'll get longer runtime, longer useful lifetime of the UPS and longer battery life.

BillP
Administrator Administrator
Administrator
0 Likes
0
143

Re: Can I maxout my UPS from time to time?

This reply was originally posted by Davide on APC forums on 2/1/2016


Isn't there a tolerance?
UPS must works until 865W as avertised by APC, will it shut down at 866W?

voidstar_apc
Janeway
Janeway
0 Likes
0
142

Re: Can I maxout my UPS from time to time?

This was originally posted on APC forums on 2/1/2016


Yes, there are tolerances. An 865W UPS will provide more than 865W. Also, the SmartUPS and maybe the BackUPS can tolerate a brief overload to accommodate inrush current. But the exact margins can vary and shouldn't be relied upon. If you care about your load staying up, pair it with an appropriately sized UPS.

BillP
Administrator Administrator
Administrator
0 Likes
0
142

Re: Can I maxout my UPS from time to time?

This reply was originally posted by Davide on APC forums on 2/1/2016


A minute of runtime is enough for me, I don't care about runtime.
I can save and close all in a minute.

With 870W load my UPS can give me up to 4 minutes of runtime, more than enough for me, as I said the runtime is not my problem, the problem is if the UPS can survive a spike of 870 or even 880W without damaging itself, my peripherals or shutting down itself for overload.

BillP
Administrator Administrator
Administrator
0 Likes
0
144

Re: Can I maxout my UPS from time to time?

This reply was originally posted by Bill on APC forums on 2/1/2016


Hi,

Any Smart-UPS 1500, 2200, 3000 can be used in the home but you need to be aware of the power requirements. Any unit that is larger than 1500 KVA will require a circuit larger than the standard 15 amp house hold circuit (U.S. standards). The larger the load placed on the UPS the larger the load that is placed on the home circuit. 

Example: SMT2200i 230 V requires input connector IEC-320 C20, Schuko CEE 7 / EU1-16P, British BS1363A

Max Configurable Power (Watts) 1.98 KWatts / 2.2 kVA