We have two TIVOs that I had a BE750G hooked to to protect for short duration. I'm pretty sure I tested that it would keep the TIVOs running during a short outtage, the unit had a new battery installed, not an APC battery, a Duracell brand, not 7AHs, instead an 8AH version. We have a whole house generator, newly installed on May 12 this year. Yesterday the power went out and the generator started and supplied power, both TIVOs felt the hit and rebooted. I only need the UPS to hold them for not more than 6-10 seconds. It did not!
I took the unit out of service and removed and checked the battery and it was just about 11 volts. I hooked the UPS to my computer via the maint connection and powershute said zero charge, BUT the unit PASSES self test.
What's going on, the battery is back at the vendor right now being tested as it's only 10 months old from manufacture date.
My thinking is the charging system in the UPS has failed and also it gave NO indication that anything was wrong, no blinking light, no beep, nothing. So if this is the case - it's there, I think all is well but I have no backup protection.
Thanks for any input anyone might have. BTW, I have 4 of these units in use at present.
Gene
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:53 PM . Last Modified: 2024-03-19 11:49 PM
Well, the UPS had a less than 1 year old battery from Batteries Plus installed. I took the battery out and down to Batteries Plus and it failed their tests and they gave me a new one.
I was worried that the UPS was not charging the battery but instead it was a bad battery. The one UPS handles 2 tivos with ease, I did the unplug test and all is well. Nothing else is connected to this UPS other than the 2 tivos.
Thanks for your input,
Gene
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:53 PM . Last Modified: 2024-03-19 11:49 PM
Passing a self test means that the UPS can switch from Online to On Battery and with the load attached, the UPS can support the load. It may not be all encompassing to detect every single possible issue and it cannot account for something like an incompatibility issue or a charger failure. Problem reporting for this type of UPS is limited.
This may not be a battery issue either. Let me type what ran through my head.
I was unclear if you had one or more units (UPS) do this. You reference one battery but said TiVos at one point making me think you had more than one UPS or maybe more than one TiVo. I couldn't tell if one UPS had a problem or more than one either depending on the answer to that first question. Based on your title, I think it is one UPS with (2) TiVos. Am I correct?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:53 PM . Last Modified: 2024-03-19 11:49 PM
Well, the UPS had a less than 1 year old battery from Batteries Plus installed. I took the battery out and down to Batteries Plus and it failed their tests and they gave me a new one.
I was worried that the UPS was not charging the battery but instead it was a bad battery. The one UPS handles 2 tivos with ease, I did the unplug test and all is well. Nothing else is connected to this UPS other than the 2 tivos.
Thanks for your input,
Gene