APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:18 PM . Last Modified: 2024-03-20 03:05 AM
Hi everyone. Please direct me to the proper area if this is not it. I have an APC Back UPS XS 1500. The sockets in the back read 115 volts when plugged in to AC but only read 88 VAC when on battery. The batteries are charged. Am I looking at a new transformer? I am new to the UPS field so be easy on me. Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:18 PM . Last Modified: 2024-03-20 03:05 AM
Thanks for the reply. Is that the reason when I plug my box fan in to check it the fan runs slower than when on line voltage? I was given this UPS and I am trying to figure it out. I don't have an extensive electrical background.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:18 PM . Last Modified: 2024-03-20 03:05 AM
Good day Neal,
It has something to do with the voltmeter that you are using. Our BackUPS provides a step approximated sine wave when it runs on battery. Non TRUE RMS voltmeters won't be able to read the exact voltage it provides but a True RMS voltmeter will. Below are some APC knowledgebase articles that would help you out.
[True RMS Voltmeter Required to Read Stepped Approximated Sine Wave|http://nam-en.apc.com/app/answers/detail/a_id/1493/kw/true%20RMS%20voltmeter]
[Different Types of Voltmeters|http://nam-en.apc.com/app/answers/detail/a_id/4119/kw/true%20RMS%20voltmeter]
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:18 PM . Last Modified: 2024-03-20 03:05 AM
Thanks for the reply. Is that the reason when I plug my box fan in to check it the fan runs slower than when on line voltage? I was given this UPS and I am trying to figure it out. I don't have an extensive electrical background.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.