hi all
i have and old smartups 2200rm xl
model SUA2200RMXLI
i change battery with new one
charged for 100 and do runtime calibration with 20% load it's just work for 6 min
i remove the load just put one lamp with 50Watte
and gharge the battery with 100% and disconnect the power source
and it's work about 7 min
so i think it's battery problem
change it with worked one and it's the same
this pic from power chute
in pic number 2 some time tell me in ups status avr boost and some time online >>??
i need it charge battery bigger from it's come with it
4 battery with 7amp i will get 4 battery with 14 or 16 amp for each one
and i found alot youtube talk about mod the code for that problem
the orginal one was 13 and i change it for 2F and many other but the same
so i need the orginal one
and i want frequency to be 60 instead of 50
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:19 AM . Last Modified: 2024-03-12 03:08 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:19 AM . Last Modified: 2024-03-12 03:08 AM
Here are a few pieces of feedback.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:19 AM . Last Modified: 2024-03-12 03:08 AM
hi
1- the boosting is not all time some time it in online mode .. i think it's weak of voltage ( EGYPT)
i could attach voltage stablizer for fix this problem
but the main problem is it's not fully charge the battery .. after 2 midnighte the voltage will be 220 stable until 11am so it's good time to fully charge without boosting mode
2-http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUA2200RMXLI3U
its show frequency from 47 to 60 So it's must be have
3- i wait for 100 charge and do calibration it's fail all led at once and refuse to do calibration
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:19 AM . Last Modified: 2024-03-12 03:08 AM
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.