how can i know if a APC UPS is an on-line or an off-line?
main UPS i worked on was on line. but i want to know if there is a way to know the type of a UPS.
can we know it, by the model? how?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:39 AM . Last Modified: 2024-03-19 12:41 AM
Our BackUPS ES Family UPS uses standby topology while our latest BackUPS Pro are uses line interactive topology. For our SmartUPS product line, those model numbers that starts with SC/SU/SUA/SUM/SMX/SMT/SMC are all line interactive, while those that are SURT/SURTA and SURTD are all double online topology UPSs.
To know more about topologies, feel free to read our [Whitepaper #1: The different types of UPS systems|http://www.apcmedia.com/salestools/archived/SADE-5TNM3Y_R7_EN.pdf]
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:39 AM . Last Modified: 2024-03-19 12:41 AM
it 's ok, thank.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:39 AM . Last Modified: 2024-03-19 12:41 AM
Our BackUPS ES Family UPS uses standby topology while our latest BackUPS Pro are uses line interactive topology. For our SmartUPS product line, those model numbers that starts with SC/SU/SUA/SUM/SMX/SMT/SMC are all line interactive, while those that are SURT/SURTA and SURTD are all double online topology UPSs.
To know more about topologies, feel free to read our [Whitepaper #1: The different types of UPS systems|http://www.apcmedia.com/salestools/archived/SADE-5TNM3Y_R7_EN.pdf]