APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:20 AM . Last Modified: 2024-03-05 02:23 AM
I am trying to upgrade the firmware for my Network Management Card in a Smart-UPS 2200XL-RM.
When I run the Device IP Configuration utility, it finds both my UPS devices with no issue.
It shows as having aos f/w rev apc_hw02_aos_361. I just downloaded the latest firmware update and ran it and
In the firmware upgrade utility, it pings successful and device connection passes but I keep getting an FTP login failed.
What am I missing? Was there somewhere for me to set up an FTP login?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:20 AM . Last Modified: 2024-03-05 02:23 AM
If FTP ports are blocked on your computer or network this could be a problem or if you've disabled FTP on the NMC. There is a setting for FTP server enabled/disabled and port in the management card. Via the web, Administration->Network->FTP.
Here is the article on upgrading firmware. You could try it manually and see if it works.
How do I upgrade the firmware on an APC Network Management Card? | FAQs | Schneider Electric US
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:20 AM . Last Modified: 2024-03-05 02:23 AM
If FTP ports are blocked on your computer or network this could be a problem or if you've disabled FTP on the NMC. There is a setting for FTP server enabled/disabled and port in the management card. Via the web, Administration->Network->FTP.
Here is the article on upgrading firmware. You could try it manually and see if it works.
How do I upgrade the firmware on an APC Network Management Card? | FAQs | Schneider Electric US
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.