Well, not completely empty, but I am missing Outlet management:
------- Device Manager --------------------------------------------------------
1- Phase Management
2- Power Supply Status
3- PDU Configuration
I upgraded from 3.7.3 to 3.7.4, but that did not fix it. Here is my current versions. Is there a version that is best for this device?
Thanks!
About System
Model Number : AP7830
Serial Number : 5A1033E00881
NMC Serial Number : 5A1032E08253
Manufacture Date : 08/10/2010
Hardware Revision : B2
MAC Address : 00 C0 B7 50 85 B5
Flash Type : AMD A29DL322DB
Press
-----------------------------------------------------------------------
Module Information
Description : Rack PDU APP
-----------------------------------------------------------------------
Name : rpdu Type : StatApp
Version : 374 Sector : 16
Date : 03/13/2012 Time : 16:16:54
CRC16 : 4D49
Press
Description : Network Management Card AOS
-----------------------------------------------------------------------
Name : aos Type : APC OS
Version : 374 Sector : 47
Date : 11/09/2011 Time : 11:45:09
CRC16 : 49C6
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:51 PM . Last Modified: 2024-03-18 11:47 PM
Hi Paul,
Your Rack PDU model shows as AP7830. AP78XX series models provide metering capability only - no switching/control of outlets. AP79XX models offer this (among some of our other Rack PDU generations/types) so AP7930 of this series would offer outlet control. This is why you don't see it in the menu and that a firmware upgrade did not change anything. Is it possible you were mistaken in thinking this was a switched model or perhaps you have another model to log into which is switched?
If you feel this is in error, you can always double check the physical strip to see what it says/shows on it for model and if it has outlet LEDs as well as if the silk screen labeling says Metered or Switched.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:51 PM . Last Modified: 2024-03-18 11:47 PM
Hi Paul,
Your Rack PDU model shows as AP7830. AP78XX series models provide metering capability only - no switching/control of outlets. AP79XX models offer this (among some of our other Rack PDU generations/types) so AP7930 of this series would offer outlet control. This is why you don't see it in the menu and that a firmware upgrade did not change anything. Is it possible you were mistaken in thinking this was a switched model or perhaps you have another model to log into which is switched?
If you feel this is in error, you can always double check the physical strip to see what it says/shows on it for model and if it has outlet LEDs as well as if the silk screen labeling says Metered or Switched.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:51 PM . Last Modified: 2024-03-18 11:47 PM
We have other apc devices: ap7900, ap7930... These have outlet control.
Thanks for informing me about the diff between metered vs switched PDUs.
Paul