APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:25 PM . Last Modified: 2024-03-19 12:09 AM
On Smart UPS SMT2200I, there are 2 ports, 1 USB and 1 RJ45 serial UPS monitoring port. Is it possible to use two ports at the same time? If I want to connect the SMT2200I UPS to one server through USB, and to another server through RJ45 serial UPS monitoring port, so that two servers can monitor the UPS at the same time, is it possible?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:25 PM . Last Modified: 2024-03-19 12:08 AM
This is how I used to run my server and NAS as the NAS only supported serial connection without plugins.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:25 PM . Last Modified: 2024-03-19 12:09 AM
Possibly not, searching the documentation on
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SMT2200I&tab=documentation
There is a link "Operation Smart-UPS 750/1000/1500/2200/3000 VA 100/120/230 Vac, 500 VA 100 Vac Tower"
that leads to this document:
http://www.apcmedia.com/salestools/SCON-7NBSEM/SCON-7NBSEM_R6_EN.pdf
where it is said: "Note: Serial and USB communication can not be used simultaneously" (Page 5)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:25 PM . Last Modified: 2024-03-19 12:08 AM
On SMT/SMX/SRT type units, it is not marketed as being possible but you can do it based on the UPS design. For older designs, like models that begin with SU, SUA, SURT, SURTA, it is not supported and will not work properly as there will be conflicts on the communication bus.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:25 PM . Last Modified: 2024-03-19 12:08 AM
Can you advise the process of connecting USB and serial to two servers. Do you just connect it and install the software or is there something more to it?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:25 PM . Last Modified: 2024-03-19 12:08 AM
Yup, there's nothing more to it, although it isn't a supported configuration.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:25 PM . Last Modified: 2024-03-19 12:08 AM
This is how I used to run my server and NAS as the NAS only supported serial connection without plugins.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.