I have an interesting little problem that I think I have found a solution to. I have a 208V 20A (L6-20) receptacle that I need to convert to 120V 20A (L5-20) and my idea is to use a APC Smart-UPS XL 3000VA 208V Tower/Rack Convertible (Link: [SUA3000XLT|http://www.apcc.com/resource/include/techspec_index.cfm?base_sku=SUA3000XLT]) to connect to the incoming line (L6-20) which then has 4 outputs, 2 x L6-20 and 2 x L6-30. I would then connect a APC 208V to 120V Step-Down Transformer (Link: [AP9621|http://www.apcc.com/resource/include/techspec_index.cfm?base_sku=AP9621]) to one of the L6-30 outlets on the SUA3000XLT to power my telcom cabinet with some L5-15 and L5-20 equipment. The SUA3000XLT will only be providing battery backup power for 10-15 seconds if the power does go out at the facility (A generator will provide backup power in an emergency).
I believe this scenario would work, but would anyone be able to confirm that?
Side note - I am not able to upgrade the 20A circuit to a 30A circuit at this time (L6-20 to L6-30).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:12 PM . Last Modified: 2024-03-15 01:24 AM
hi,
i think this will work fine but the only thing you need to worry about is the 20 amp breaker on your UPS is what will limit your power/current draw. the 30 amp outlets on that UPS are for convenience only and even though are 30 amp receptacles, it is still limited by the 20 amp breaker/plug type on the UPS. same applies to the step down transformer. it has a 30 amp plug but you cant pull that much since the UPS breaker/plug tpe limits your current draw.
as long as you keep all of this stuff under 16 amps (because of the plug on the UPS and the 80% national electrical code rule), you will be fine.
let me know if you have any other questions.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:12 PM . Last Modified: 2024-03-15 01:24 AM
hi,
i think this will work fine but the only thing you need to worry about is the 20 amp breaker on your UPS is what will limit your power/current draw. the 30 amp outlets on that UPS are for convenience only and even though are 30 amp receptacles, it is still limited by the 20 amp breaker/plug type on the UPS. same applies to the step down transformer. it has a 30 amp plug but you cant pull that much since the UPS breaker/plug tpe limits your current draw.
as long as you keep all of this stuff under 16 amps (because of the plug on the UPS and the 80% national electrical code rule), you will be fine.
let me know if you have any other questions.