APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:35 AM . Last Modified: 2024-03-12 11:21 PM
Can anybody help me to find out
what does this message mean?
Smart-UPS RT 5000 XL
Serial Number : ZA1125003965
error Code : 0x0154
thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:35 AM . Last Modified: 2024-03-12 11:21 PM
please take a look for additional attached in EN
now voltage rating is OK
but it happens time by time
and I have to know about reason
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:35 AM . Last Modified: 2024-03-12 11:21 PM
Can anybody help me to find out
what does this message mean?
Smart-UPS RT 5000 XL
Serial Number : ZA1125003965
error Code : 0x0154
thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:35 AM . Last Modified: 2024-03-12 11:21 PM
This means the battery voltage in your UPS is high. Nominal refers to normal or expected and for a Smart UPS RT that you have, the nominal battery voltage is 192vDC and it floats at around 211-218vDC.
You could start by providing the logs (event.txt and data.txt) from your network management card for us to review and assist. Instructions on doing this are here ->How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...
I'd also maybe suggest someone maybe do a visual check on the batteries to ensure they are not damaged then reviewing the logs will tell us more.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:35 AM . Last Modified: 2024-03-12 11:21 PM
please see attached files (notice that event in RU lang, I hope it is not a problem cause all error codes are international)
visually batteries is OK
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:35 AM . Last Modified: 2024-03-12 11:21 PM
I can try to read the data logs at least but the event log will take me longer to go translate the event codes. Could you change web UI to english and download the logs then switch it back?
I could see in the data log at least that there was a very high battery voltage of 235VDC at one point (12.08.2013 | 14:40:07). Seems like the time frame you were referring to?
I'd have to see what could cause this type of thing but it appears to be back to normal now.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:35 AM . Last Modified: 2024-03-12 11:21 PM
Hello,
all batteries were replaced and we have no problems from that time
thanks a lot
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:36 AM . Last Modified: 2024-03-12 11:21 PM
Are these the original batteries? I will do some further investigation today.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:36 AM . Last Modified: 2024-03-12 11:21 PM
In reviewing the files further with the Smart UPS folks here, we have to believe this is an issue with the batteries themselves as there is no evidence pointing to anything else. You can try contacting your local technical support to verify warranty status to see if the UPS is under warranty and therefore, we'd be able to send you replacement batteries if that is the case. If it is not in warranty, I'd still suggest replacement batteries at this time as a first step.
The phenomenon of the high voltage on the batteries always seems to follow an on battery event of some type (power blip, UPS self test) so I also noted that.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:36 AM . Last Modified: 2024-03-12 11:21 PM
we have 2 Smart-UPS RT 5000 XL
both of them with the same error and under warranty till okt of 2013
please notice that they use 2 additional APC Smart-UPS RT 192V Battery Packs may be the problem is in it?
how can we get replacement batteries?
thanks a lot
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:36 AM . Last Modified: 2024-03-12 11:21 PM
It could be the battery packs - anything on the battery bus. If you're under warranty, you'll need to contact your local technical support via phone or email and then they'll verify the warranty and then they'd decide which batteries they can and will replace under warranty for you. Strange that two of them have the same issue...
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.